- Reaction score
- 2
Discuss Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net
Hi, can anyone offer any advice as to why the heating would run when HW is called for?View attachment 60012
Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installedMore often than not its becuse the zone valve on your heating has failed open.
Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installed
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installed
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.
Based on the wiring center diagram you've posted you have a conventional system boiler.
You will have one, two (or even 3) zone valves as per the pictures bellow.
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.
Hi, can anyone offer any advice as to why the heating would run when HW is called for?
No, the wiring diagram posted does not show a conventional system boiler with zone valves.
The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]
According to the picture it is a two pump system, no motorised valves are used with this.
No, the wiring diagram posted does not show a conventional system boiler with zone valves.
The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]
According to the picture it is a two pump system, no motorised valves are used with this.
[automerge]1596964649[/automerge]
It is impossible to say from just that diagram.
Haa it always worked this way or is it a fault which has developed recently?
Does the room thermostat have any effect when the CH has come on via the hot water controls?
Unfortunately the wiring diagram is incomplete, it doesn't show the internal links between the connections so we can only guess at what the full circuit is.
Without further information this needs to be tested by a good electrician.
I apologies, your right, I didn't look closely enough at the diagram to see the second pump. I didn't even know such a system existed, I've seen gravity hot water but never a second pump.
Surely without a valve both systems will always heat up?
If there are no valves in the system a blockage in the hot water flow/return may well force flow through the heating circuit instead.
This is the old wiring centre, we assume it has always worked correctly. Please not that on the picture if there is a notch then the terminals have a link. We have rewired the property but kept the heating system as was just renewing the cabling. Could the frost stat cause an issue if set to call for heat?
Thanks for your message.Ah, so you are an electrician working on the system, your OP gave the impression of a fault finding situation on an existing installation, not that you'd interfered with the wiring and messed it up.
My first question has got to be why did you mess with a working system?
Did you not take the time to investigate and understand the control system before you took it apart?
Did you test the system before taking it apart to ensure you understand how it is supposed to work and whether or not it was working correctly?
You have the old wiring centre and the wiring diagram so you can work backwards from this to draw yourself a diagram of how it was connected previously. From this you can work out how the system is supposed to work and then start to fault find.
Thanks for your message.
My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?
Thanks for your message. I am back on the job tomorrow. I will what you have suggested ?Do the pumps stop and start in response to demand from the two thermostats/time clock?
If you connect a switched live to the boiler and temporarily connect power the pump bypassing the controls does the issue go away?
If you fire the boiler and run only one pump and the other circuit heats up that would imply its a piping design/plumbing fault rather then a an electrical issue.
Heating systems used to be entirely gravity fed using only the fact cold water is more dense than hot water. It may be your getting effects such as these.
Thanks for your message.
My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?
I am back on site tomorrow Dave, I will see what is happening and if unable to resolve I will send a diagram of the installed system. Thanks for your messageSo can you post the wiring diagram you have created of the old system? Or describe its operation?
Can you also post the wiring diagram of what you have installed?
You haven't given enough information to be able to offer any helpful advice as far as I can see.
A diagram of what you have installed will allow us to see how it is currently operating and suggest how to achieve the desired operation.
I have given all the advice I can confidently give without further information.
I could offer you a bunch of random guesses at what might be wrong, but that wouldn't help.
I've sketched what I would expect the basic control circuit to be for a standard (non overrun) boiler with a two pump system.
View attachment 60036
This would not be for a pump overrun boiler.
Hi Dave,
Whats the purpose of the relay?
To create a common switched live without both pumps interacting?
. Then there was the SMC controller 3-port pump. Anyone remember those?
I don't know why dual pumps are not more popular. Given how long the better pumps last and how unreliable zone valves tend to be, I've always thought it a good idea. I put a dual pump system in 20 years ago for someone who was fed up with valve failures, and AFAIK both original pumps are still going. And in the days before intelligent pumps you could set the HW pump low and avoid having a bypass regulator. Then there was the SMC controller 3-port pump. Anyone remember those?
Two other issues are that modern bookers generally provide a pump overrun feature, thus allows the heat exchanger to Bd cooled after burner shutdown. To do this with two pumps requires a specialist programmer which appear to be fairly hard to come by.
Why on earth would you need a specialist programmer to allow a pump overrun? The programmer doesn't feature in the pump overrun at all.
All it needs is a relay to connect one of the pumps to the overrun terminal when there is no demand on the boiler switched live. The grundfoss pump plan included this in the simple, easy to connect wiring centre supplied with it.
I don’t know, you’d have to ask why Grundfoss decided to do it that way. The fact a relay in a box with wiring would require CE certification in order for it to be legally sold probably puts it beyond the scope of your average domestic electrician/heating engineer.
The CE certification is the manufacturers problem, not the installer.
One difference is where goods are imported from outside the EU, on which occasion the importer becomes liable for ensuring that goods are compliant. Not an everyday issue for most electricians, but potentially worth keeping in mind when sourcing items for those more unusual jobs.
What has that got to do with this?
I stated that grundfoss supplied a wiring centre which included the relay required for the pump plan system and now we are wandering off in the rhubarb talking about CE marking!
The CE certification is the manufacturers problem, not the installer.
If you buy a number of electrical components and integrate them into an assembly or enclosure you are then classed as the manufacture of that assembly.
Irrespective of if the commoners used are CE marked the assembly as a whole must go through a product safety/conformance process.
Reply to Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net