Discuss High integrity earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Guest 004

Can anybody here give some examples of this, and in what situations it would be used?

More importantly my understanding is that you would need an extra bar at the DB, which is then maybe insulated?
 
Most commonly found in IT suites due to the high earth leakage current of the equipment associated with them.

543.7 refers.

Also see attached PDF.
 
Last edited by a moderator:
The extra bar at the DB is not really that necessary, I don't quite know what you mean by insulated.
Obviously it will be insulated from any live conductors or bars.
There are two methods for providing high integrity earthing.
one is to use a substantially larger CPC than is normally used, the other is to use a second CPC.
When using a second CPC, the conductors should be terminated in different terminals from those for the first CPC.
This is where a second earth bar would be used, if ther is only one earth bar, then the usual practice is to terminate the second CPC in the terminal next to the first CPC. This will often entail doubling up conductors with those of a different circuit.
 
The extra bar at the DB is not really that necessary, I don't quite know what you mean by insulated.
Obviously it will be insulated from any live conductors or bars.
There are two methods for providing high integrity earthing.
one is to use a substantially larger CPC than is normally used, the other is to use a second CPC.
When using a second CPC, the conductors should be terminated in different terminals from those for the first CPC.
This is where a second earth bar would be used, if ther is only one earth bar, then the usual practice is to terminate the second CPC in the terminal next to the first CPC. This will often entail doubling up conductors with those of a different circuit.

well that differs from the pdf doc
 
Does it?
I'm not really suprised, as from glancing at the document I note that it is written by Mark Coles.
I'd suggest that rather than relying on Mark's opinions, you have a look at Section 543.7 in BS7671.
 
the pic on page 10 is useful. also, you would use socket outlets with 2 earth terminals and connect 1 cpc leg to each, rather than the more usual way of puuting both in 1.
 
the pic on page 10 is useful. also, you would use socket outlets with 2 earth terminals and connect 1 cpc leg to each, rather than the more usual way of puuting both in 1.
The two terminals are intended for two separate CPCs, one CPC in one terminal and the other CPC in the other terminal.
If only one CPC is being used, there is no need to use socket-outlets with two terminals.
 
Last edited by a moderator:
The two terminals are intended for two separate CPCs, one CPC in one terminal and the other CPC in the other terminal.
If only one CPC is being used, there is no need to use socket-outlets with two terminals.

hmm, i was taught , rightly or wrongly, that if, say, the circuit was a ring final, then you used both terminals in case of a break in 1 cpc, i'll have a read of 543.7, the guy that tol,d me the above, however, was adamant that fly leads must be fitted to back boxes. tbh, it's not something i come across , so have not bothered to research hi integrity earthing fully.
 
"543.2.7 Where the protective conductor is formed by conduit, trunking, ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accesory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure."
"543.7.1.4 Where two protective conductors are used in accordance with Regulation 543.7.1.3 (iii), the ends of the protective conductors shall be terminated independantly of each other at all connection points throughout the circuit, e.g. the distribution board, junction boxes and socket-outlets. This requires an accessory to be provided with two separate earth terminals."
 
Last edited by a moderator:

Reply to High integrity earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

For the bathroom, want them matching and one needs to go over the shower. Also need to be ok with insulation over the top. Ideally fit in the...
Replies
2
Views
232
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
671
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock