Discuss High(ish Zs and extending ring final question. in the UK Electrical Forum area at ElectriciansForums.net

Marcus Vaughan

-
Esteemed
Reaction score
240
Hi all. Love the forum by the way.

I do have a question though...

I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper.

Thought I’d better do a live Zs test.

Zs = 1.29, down to 1.22 back of socket. Checked a nearby socket - same results.

So it doesn’t comply with Max Zs values for ADS and I am not one of those who likes to use the ‘RCD get out of jail card’.

So by extending it I will be knowingly making the circuit less compliant.

Impractical to split circuits (no room in the CU). Impractical to rewire in larger cable.

Feels like a no-go.

I was wondering if, with those values, it would make enough difference if I conducted the dead test for more accurate results?

Clutching at straws.

Flooring going in Wednesday apparently....

Irony is that I know they will just use extension leads across the floor instead.

I wonder what you would do?
 
You should properly dead test the circuit before you can make any decisions - starting with the Ze and then the end to end readings of the circuit..

If those are the true readings, maybe consider dropping the breaker to 20A .....
 
Thanks for quick replies. I had something similar before. I managed to change the MCB to 25amp. But then worrried that I had compromised on 433.1.204 - that is to say that ring finals MUST be protected by 30 amp or 32amp.

Reading it through again - I see the words ‘may be supplied...’. So technically we are not breaking the reg.

Are we?

No issues with loading.
 
Do your dead tests and calculate the Zs and compare with live readings. If the calculated is much lower you may have a high resistance somewhere, for eg I have heard some RCDs can do this.

Hi Andy, I was hoping you would chip in. Thank you.

That makes sense to me. The circuit doesn’t seem particularly long. The RCD is suspicious - tripping on live tests. Though RCD tested OK - including Ramp Test.

I think I would prefer to at least know that I can change the MCB if I need to - without falling foul of regs.
 
Hi all. Love the forum by the way.

I do have a question though...

I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper.

Thought I’d better do a live Zs test.

Zs = 1.29, down to 1.22 back of socket. Checked a nearby socket - same results.

So it doesn’t comply with Max Zs values for ADS and I am not one of those who likes to use the ‘RCD get out of jail card’.

So by extending it I will be knowingly making the circuit less compliant.

Impractical to split circuits (no room in the CU). Impractical to rewire in larger cable.

Feels like a no-go.

I was wondering if, with those values, it would make enough difference if I conducted the dead test for more accurate results?

Clutching at straws.

Flooring going in Wednesday apparently....

Irony is that I know they will just use extension leads across the floor instead.

I wonder what you would do?


With the earth loop reading, this would be fine with an RCD fitted, take a LN loop test to see if it meets short circuit protection for the device being used, if not just down rate the protection device to suit.
 
With the earth loop reading, this would be fine with an RCD fitted, take a LN loop test to see if it meets short circuit protection for the device being used, if not just down rate the protection device to suit.

Not sure if I agree with this ..... I would say further investigation IS required .... relying on RCD's isn't a "get out" IMHO
 
Not sure if I agree with this ..... I would say further investigation IS required .... relying on RCD's isn't a "get out" IMHO

Totally agree with @Murdoch . Simply saying 'drop the MCB rating' or 'rely on the RCD for fault protection' isn't good enough.

Dead tests should be carried out (as already stated) and used to determine where the cause of the high Zs is. Could be the earth for the whole installation is bad requiring DNO intervention, or a bad connection somewhere on the RFC.

And no, you're not breaking the regulations by using a lower rated MCB for an RFC. As the designer you can elect to do that.
 
Yep. Just seen one on ebay. 25 amp.
Not a huge fan of 2nd hand breakers but this is probably the lesser of all evils.

I think I’ll try and persuade the customer that I should dead test and if still necessary search for anything that might be causing the readings. I should also warn him that I might need to change the MCB.

Sounds like a plan.

A bit short of time though....

Pressure is on!
 
Perhaps I need not worry too much about mix and match manufacturers in the consumer unit. Just noticed on my photo there is a Hager to the right and a Wyler to the left.

Yuk.

7EB3DDB1-F70A-4536-9E12-0CF4668D2CE8.jpeg
 
Sometimes you do get a “high” Zs reading when testing a circuit with an RCD. I’ve had this happen before and out of curiosity have bypassed the RCD or put the lives into the non RCD side, and the results have been a lot lower.
As the others have mentioned, do the ring dead tests and that will highlight any connection issues.
 

Reply to High(ish Zs and extending ring final question. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
287
I have a customer that requested kwh meters on the socket circuits of an office lock he rents out,(rooms are rented separately). There are two...
Replies
14
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
683
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock