- Reaction score
- 240
Hi all. Love the forum by the way.
I do have a question though...
I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper.
Thought I’d better do a live Zs test.
Zs = 1.29, down to 1.22 back of socket. Checked a nearby socket - same results.
So it doesn’t comply with Max Zs values for ADS and I am not one of those who likes to use the ‘RCD get out of jail card’.
So by extending it I will be knowingly making the circuit less compliant.
Impractical to split circuits (no room in the CU). Impractical to rewire in larger cable.
Feels like a no-go.
I was wondering if, with those values, it would make enough difference if I conducted the dead test for more accurate results?
Clutching at straws.
Flooring going in Wednesday apparently....
Irony is that I know they will just use extension leads across the floor instead.
I wonder what you would do?
I do have a question though...
I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper.
Thought I’d better do a live Zs test.
Zs = 1.29, down to 1.22 back of socket. Checked a nearby socket - same results.
So it doesn’t comply with Max Zs values for ADS and I am not one of those who likes to use the ‘RCD get out of jail card’.
So by extending it I will be knowingly making the circuit less compliant.
Impractical to split circuits (no room in the CU). Impractical to rewire in larger cable.
Feels like a no-go.
I was wondering if, with those values, it would make enough difference if I conducted the dead test for more accurate results?
Clutching at straws.
Flooring going in Wednesday apparently....
Irony is that I know they will just use extension leads across the floor instead.
I wonder what you would do?