Maxstone89

Hi all

I have a house where all the circuits meet the Max Zs for that circuit yet the lighting circuit is testing as 747 ohms Zs

It looks like it used to be a TT system and been converted to a TN-C-S system. As its also got an main tcd before the board. Could this somehow be causing this high reading, even though the lighting circuit is connected to the main pme where all other circuits are or is their other possibilities.

Thanks max
 
What are the dead test continuity results for this lighting circuit? These readings will help determine why you have a high Zs.
 
Ran out of time, so gotta go back to sort other problems out so i am going to dead tests then, any ideas to give me a heads up.

Would be appreciated

Regards Kurtis Randle
 
Hi all

I have a house where all the circuits meet the Max Zs for that circuit yet the lighting circuit is testing as 747 ohms Zs

It looks like it used to be a TT system and been converted to a TN-C-S system. As its also got an main tcd before the board. Could this somehow be causing this high reading, even though the lighting circuit is connected to the main pme where all other circuits are or is their other possibilities.

Thanks max

Ran out of time, so gotta go back to sort other problems out so i am going to dead tests then, any ideas to give me a heads up.

Would be appreciated

Regards Kurtis Randle

Ok mate let's start with who you are. Post #1 you're called max and post #3 you're Kurtis Randle. View Profile: Kurtis.Randle@m - Electricians Forum | Electrical Advice Forum | An electrical forum for electricians in the UK This leads me to believe you have opened a duplicate which is against forum rules. Let me know which name you want to use and I will merge the 2 accounts.
 
I was wondering if it had a earth. So I Google how to measure Zs without an earth, found a chat on ITE talking how...



John Peckham
"I think you can get a special meter for measuring Zs on a circuit without a CPC. I have not seen one of these meters and I do not know how they work however I have seen Zs readings on PIRs for circuits without a CPC! "
 
Last edited by a moderator:
this special meter he refers to is "make it up. client only wants a satisfactory report for £50."
 
a R2 from CU to each point would help. easiest way is to go to each switch for starters.
 
this special meter he refers to is "make it up. client only wants a satisfactory report for £50."

Maybe cash to be made there... Just a circuit with a timer to get a random number for Zs that is under what you need.
We could stick to probs on to make it look goos and a test button to set the random figure off
 
Will be going back if customer will pay, but if he wont would any of you guys class this as unsatisfactory on a eicr even if there is an rcd protecting the full board?

If their was no rcd i wouldn't pass it but as there is and the result is below 1660ohms for a 30ma rcd cant remember exact figure would you pass it and add a note of recommendation?
 
If you have 747Ω as the resistance of a domestic circuit then there is something very wrong, this is equivalent to a 60W light bulb connected through the cpc.
Even though it does meet the 1667Ω requirement for a 30mA RCD it is very likely that you have a very poor / corroded connection somewhere (or a major wiring error) and that this will get worse over time.
There is no sensible way this can be a result from a satisfactory circuit.
The fault needs to be identified and resolved.
However if the customer does not want to do it then you do have to leave it, but I would recommend putting an advisory of a faulty circuit in writing.
 
I would guess.the problem is, did you measure some thing wrong and it looking daft on you

Maybe do.it for free to make sure you didn't cook up
If you did cook up some way it would look like your trying to con the person
 
If you have 747Ω as the resistance of a domestic circuit then there is something very wrong, this is equivalent to a 60W light bulb connected through the cpc.
Even though it does meet the 1667Ω requirement for a 30mA RCD it is very likely that you have a very poor / corroded connection somewhere (or a major wiring error) and that this will get worse over time.
There is no sensible way this can be a result from a satisfactory circuit.
The fault needs to be identified and resolved.
However if the customer does not want to do it then you do have to leave it, but I would recommend putting an advisory of a faulty circuit in writing.





Thanks
 
Last edited by a moderator:
I would guess.the problem is, did you measure some thing wrong and it looking daft on you

Maybe do.it for free to make sure you didn't cook up
If you did cook up some way it would look like your trying to con the person

Whats with the sarcastic remarks.
Please do not comment if its gonna be sarcasm.
 
Whats with the sarcastic remarks.
Please do not comment if its gonna be sarcasm.

I think Duane was just thinking out aloud there and was not trying to be sarcy... He was just saying are you 100% that the test result is the correct one given all others are OK. We all makes mistakes from time to time after all. I can see Duane's point that if it was a mistake then it could look like you were creating work.
 
Fair enough, just the amount of people being sarcy on here is just daft, so if you weren't then no worries.

Yes all the readings on both light citcuits where all coming out at the same which is odd.
 
So, there is TWO Circuits, two MCBs 6A about, and all the Light Points the Zs is 747Ohms when you need Zs Max of 7Ohms (5A) and 5.87Ohms (6A) I think [NB i put i think, as someone may correct me]
So 747Ohms is not great even if it was 7.47Ohms still above the Max Zs

As Zs = Ze + R1 + R2 , if R1+R2 is Dam high you know the fault is on it, which would be the logical thing
But any thing could happen i guess, could be lose wires hangin in a pool of water, or just hold on by one strand.

Sounds a bit like someone has wiring a Light bulb in series, Live to Bulb to Light Sockets, then as long as one light comes on you wil get the light on, but would give you a high ohms reading.



I know your with NICEIC (looked up on your other account
NICEIC Consulting
Tel: 0500 600 545
Email: [email protected] - See more at:

Im not one who can be
sarcasm because of my problems, it will just blow back at me.
I can be dam Strange like the Uniform YCMA Post, and As you Noticed the Zs Test without a CPC, what you know is impossible but people still get figures for, so i googled it and someone JOKED about a Meter that could measure it.
But as your results, I understand wanting to get every thing perfect and when things aint spot on, one can tend to get worried. I do JOKE to Try and Lighting the mood, im like that in Group Orgies too, ----ing a Coin heads of tails for what end one gets.
 
Last edited by a moderator:
So if customer doesnt want a return visit, do i code it c2 on eicr or as it has an rcd or c3?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks
 
Last edited by a moderator:
So if customer doesnt want a return visit, do i code it c3 as it has an rcd or c2?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks

What do you mean by a return visit? What exactly is the job you are doing here?
 
Carrying out an Eicr.

I have possible ideas why which some have been stated, just thought why not ask in case a simpler answer/possible cause is out there
 
So if customer doesnt want a return visit, do i code it c3 as it has an rcd or c2?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks

I'm assuming that you are undertaking a PIR here,

Whether the customer wants a return visit or not is not the point, you've carried out an inspection so you must code as you see fit.
Also you can't code as you would a different system, the earthing system you have is what you must assess the installation on.

For what it's worth, providing I've understood correctly I would give this a code 2.
 
Carrying out an Eicr.

I have possible ideas why which some have been stated, just thought why not ask in case a simpler answer/possible cause is out there

Right, it's an EICR so you are there to carry out the tests, record the results and make your decisions about coding, you would not normally be there to do any investigation of the faults.

You have a Zs result which is abnormally high considering the supply type (TNCS) so there is a very strong possibilty that there is a fault there and it's not just a circuit with a high Zs. So I would be inclined towards a C2
 
Would anyone else code it C1/C3??

I think C2 seems correct, just always worth asking other people's opinions and thoughts how they have come to it.
 
it's a C2 in my book. ( an exposed part could become live under fault conditions. with no cpc, then this could be lethal.) with a comment that further investigation is required.
 
not in my book. with a reading of 700 odd ohms, that could easily become >1667 ohms and so negate the use of the RCD as fault protection. C2 all day.
 
I would be putting a C2.

If it had been a TT then perhaps a C3 if it had a thick, deep, stable earth rod or perhaps mulitiple earth rods. But if your other Zs figures meet the required figures and this 'one' doesn't then I guess the earthing arrangement must be as you have stated (PME), so I would say a C2.

I find it strange when I put down a C2, or perhaps multiple C2's and the customer doesn't get back to you! This has happened twice and I know for certain that on one occassion they have not had the work carried out.
 

Reply to High Zs on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
703
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
509
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock