Discuss High Zs values (Just) in the UK Electrical Forum area at ElectriciansForums.net

to throw the cat into the pigeon coop........ so we are believing that a , say, 0.4 sec. disconnection time cannot be achieved if the Zs of a circuit is a fraction of an ohm above the BS7671 ( corrected, Cmin etc.). who's to say if this is dangerous, or potentially dangerous? how can anyone assume that a person in contact with a "live" exposed part and an extraneous part cannot endure a touch voltage of <50V for a split second longer without dying? have the IET done some tasting on animals to prove or disprove? or is it a case of "let's make something up to justify new regs./amendments?
 
Why was this Cmin not come to light years ago it must have always been something to take into account.
You know what will happen next, although in the table it gives maximum Zs values they will write a new reg that states any new circuit must be designed to a max percentage of that to give allowances.
 
to throw the cat into the pigeon coop........ so we are believing that a , say, 0.4 sec. disconnection time cannot be achieved if the Zs of a circuit is a fraction of an ohm above the BS7671 ( corrected, Cmin etc.). who's to say if this is dangerous, or potentially dangerous? how can anyone assume that a person in contact with a "live" exposed part and an extraneous part cannot endure a touch voltage of <50V for a split second longer without dying? have the IET done some tasting on animals to prove or disprove? or is it a case of "let's make something up to justify new regs./amendments?
Not sure you can write that on your report tho :)
If you can’t guarantee the disconnection times quoted by the regulations by using the generic time curves or the manufacturers data for their OCPD’s then you can’t fully comply with the regulations regarding fault protection.
 
I'm not going to argue with anyone who advocates a code 2. That's an interpretation which can be justified. But my interpretation is that a compliant circuit is not safe one day and potentially dangerous the next simply because some boff playing with figures moves the goalposts to justify his existence.
However as already stated I will discuss the issue with my NICEIC inspector on his next visit and if he thinks a code 2 is appropriate then that's what I'll do in future...…(through gritted teeth mind you)
 
I'm not going to argue with anyone who advocates a code 2. That's an interpretation which can be justified. But my interpretation is that a compliant circuit is not safe one day and potentially dangerous the next simply because some boff playing with figures moves the goalposts to justify his existence.
However as already stated I will discuss the issue with my NICEIC inspector on his next visit and if he thinks a code 2 is appropriate then that's what I'll do in future...…(through gritted teeth mind you)
Keep us updated if you don’t mind if your inspection is anytime soon?
Would be interested to hear another opinion on it
 
For me it's C2 on a report (sorry). Getting very imaginative - the "fix" could be a temperature and load study proving headroom in the 80% factor, but only in a managed installation. This would then be written onto EIC as a deviation.
 
to throw the cat into the pigeon coop........ so we are believing that a , say, 0.4 sec. disconnection time cannot be achieved if the Zs of a circuit is a fraction of an ohm above the BS7671 ( corrected, Cmin etc.). who's to say if this is dangerous, or potentially dangerous? how can anyone assume that a person in contact with a "live" exposed part and an extraneous part cannot endure a touch voltage of <50V for a split second longer without dying? have the IET done some tasting on animals to prove or disprove? or is it a case of "let's make something up to justify new regs./amendments?
I did some tasting on a couple of animals last night. I had a chicken and lamb curry, it was delicious.:D
 
I have bowed to the inevitable and issued the EICR with a code 2 for the high Zs. While I still do not agree I've no doubt the NIC will say a code 2 and that seems to be the majority view on here. Remedial will only involve changing a type C for a B, which will no doubt prompt comments about why bother making a fuss. Well I like coding to be correct and justified on my reports regardless of the cost of rectification.
 
I think you are taking the correct action in both cases, code 2 for the New World Order, and feeling that you do not agree but want to get things correct and justified.
The risk assessment would say
Hazard: long disconnection time
Likelihood: 0.0001%, low 1,
Effect: death, high 5.
Risk assessment overall 5, low risk, no action to take, no control measures required.
Overruled by IET random thoughts.
Full control measures to be implemented.
 
I'm not going to argue with anyone who advocates a code 2. That's an interpretation which can be justified. But my interpretation is that a compliant circuit is not safe one day and potentially dangerous the next simply because some boff playing with figures moves the goalposts to justify his existence.
However as already stated I will discuss the issue with my NICEIC inspector on his next visit and if he thinks a code 2 is appropriate then that's what I'll do in future...…(through gritted teeth mind you)

Why don’t you stick by your guns if you are so certain? What is it about your NICEIC Inspector that you respect so much?

If I was certain of ny stance I would be telling the NICEIC what I am doing not asking them if I can.
 
Mostly because inconsistencies in coding is an issue for recipients of EICR's. I think consensus and following established guidelines is important for an EICR to be credible, the worst EICR's I have seen are where the inspector has applied his own prejudices. I recall one where neutrals in a switch box had been given a code 2.
 

Reply to High Zs values (Just) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock