Kenny.

Right Ladies and Gents I would appreciate your input on this one, I've been asked by a customer to repair some defect highlighted by a recent EICR carried out by a large industrial inspection company.
The plant in question is fed from a 200kVA Genny.
4 of the defects are related to high Zs reading on sub main CP's, All are protected by Merlin TP 32A type D's, the highest reading I recorded was 0.37 ohm, obviously above the requirement of the BGB but below 0.51 ohm stated on Schneider's web site.


The other contributing factor I noticed was when carrying out the loop tests the Genny main switch tripped, whipped the cover off and there's no noticeable RCD but there is control wiring going to the switch so there could be a UVR coil or a shunt release in there and a RCD somewhere else in the circuitry.
A ramp test showed the Genny tripping at 350mA and a time of 38.8 at 500 mA. Surely if it has an RCD table 41.5 applies What should I do next ?
Thanks Ken
 
Only talking from memory here, but as far as i know a 32A Type D breaker has a max of 0,37 ohm Zs. also remember that manufacturers requirement data is far more accurate than those given in the BGB, which are in essence, coverall guidance figures...

Not sure about the earth leakage side of things, maybe there is a protective relay in there somewhere. Don't you have any manufactures manual for this Gen-set??

As i say that 0.37 ohm is only from memory, i have no reference data with me to hand... lol!!
 
I worked on a genny that had an extra ct around one phase and another on the neutral. This went back to a small module where you change the settings for mA and for time delay. This then activated the shunt trip coil in the main switch when it needed to.
 

Reply to High Zs's on a Genny in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K
an eicr was carried out to an industrial plant area were the zs readings were all high readings above the maximum for a tns installation i...
Replies
9
Views
2K
Testing SWA 16mm sub main to a garage, getting reading of 66 ohms between R1+R2 and a IR resistance of between 4-5 M Ohms anyone explain how? The...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock