Discuss History of PME Systems. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Cheaper to install than running a separate earthing conductor along side the supply.
As for when, I don’t know late 70s perhaps?
 
But the old cables were lead sheath? They didn’t have a separate earth conductor. The lead would have added a cost though I suppose.

Is that the only reason? Just cost?

And what the danger of a lost N, why did they think this was safe?
 
Lost n will be discovered very fast. Lost e would not be. So it makes sense to combine as long as you trust your equipotential zone and bonding.
So you could say pme was a safety improvement, a bit like putting your smoke alarms on the lighting circuit.
Has anyone got figures for death by pme Vs death by tn-s?
 
The lost Nuetral could go undetected forever though because of the bonding as long as the pipes that are bonded are actually extraneous in that case the installation may well be using the bonding to the gas and water pipes as a nuetral...
 
And if the pipes are not bonded, appliances and everything metal that’s connected to a CPC becomes live. That’s not an improvement. But as you say, you’d need to trust your equipotential zone.
 
The lost Nuetral could go undetected forever though because of the bonding as long as the pipes that are bonded are actually extraneous
Would that not be obvious due to high resistance neutral?
And if the pipes are not bonded, appliances and everything metal that’s connected to a CPC becomes live.
as you trust your equipotential zone and bonding
Yes no bonding would be dangerous
 

Reply to History of PME Systems. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Replies
3
Views
548
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
547
Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
362
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
557
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock