Hi

I know this has been done to death, but was looking for some definitive opinions.

Eg 6mm t+e 4kw double oven 7kw hob 32a MCB or 40a MCB

From searching the forum it appears acceptable to connect both appliances to a single supply bearing in mind diversity.

It has been stated that 2.5 hr flex for oven and 4mm for hob connected to outlet plate.

The 32a MCB would not protect the 2.5 for overload (unlikely) but would for short circuit.


If the manufacturer has no requirement for MCB sizing is the above acceptable? I.e. were protecting the external cable not the load.

However if the manufacturer states 20a ocpd would it be necessary to add a cu to split cable and provide this.

I've seen it done both ways , a recent kitchen install 20a double oven 45 a dp switch, 6 mm cable 40a MCB.


A lot of appliances Bosch Siemens neff now supplying combined ovens, micros etc as 16 a how does everyone supply these especially a a retro fit.

Sorry for rambling post hope you can extract what I'm asking.
 
You should start with what the manufacturer recommends in terms of electrical connections for each appliances. The oven comes supplied with 2.5mm flex?
 
This is usually a question that still splits the forum, I sit in the park of suitable wiring for max demand without diversity.

Diversity in domestic is for total KVA demand on the supply not for final circuit design, if you are able to switch on all oven and hob loads on together then your cable should be suited to that possibility.

You could wire in say 10mm 'calcs' permitting and use a dual cooker outlet thus acheiving the 1 circuit design, the oven and hob can be classed as fixed loads as long as you circuit can handle both max plated loads together thus only requiring S/C protection for the reduced flexes to the hob and oven.
 
Think you would be pushing the limits for protecting a 6mm tw&e with 40amp mcb, unless it was clipped direct etc. What are your calculations for total loads for each appliance, after applying diversity, or does the manufacture state max load for each appliance? (appreciate they often state total max load, as opposed actual max load)
 
Some manufacturers will state total max load, their appliance can draw at any one time, e.g. ovens can generally only have fan oven or top & bottom grill on at anyone time. Hobs can physically have all four hobs on at once, but someone here will be able to explain thermostats switching etc. I never known a standard separate oven/hob set up need more than 6mm & 32amp MCB or cause it to trip.
 
think 10mm Cable looking at 45A what is about 10KW and your MAX is 11KW

as someone said 6mm you would have to have it CLIPPED to WALL for it be able to handle 45A
so 6mm would be around 32A range, IV, looking 7KW range
 
think 10mm Cable looking at 45A what is about 10KW and your MAX is 11KW

as someone said 6mm you would have to have it CLIPPED to WALL for it be able to handle 45A
so 6mm would be around 32A range, IV, looking 7KW range

hum......

Our cooker has a "theoretical" combined load of 17.7kw - yet the manufacturers state the cable minimum to be 6mm T&E!
 
This is usually a question that still splits the forum, I sit in the park of suitable wiring for max demand without diversity.

For a domestic cooking load? This has been tried and tested over and over again, the diversity calculations work for the final circuit design in this case.

Even the 'what if they're cooking chris as dinner' line which gets rolled out every time is nonsense. There's no way every element will be switched on at the same time, you don't start cooking the turkey at the same time as the vegetables!
 
hum......

Our cooker has a "theoretical" combined load of 17.7kw - yet the manufacturers state the cable minimum to be 6mm T&E!
I was looking at the Current Carrying Capacity Tables 6mm Clip to wall it says 46A, as you know 230v x 46A = 10580W
not taking in to account any voltage drop.
 
hum......

Our cooker has a "theoretical" combined load of 17.7kw - yet the manufacturers state the cable minimum to be 6mm T&E!


Can this ever happen though - some designs limit the actual loads that can be on together with selection switches etc, I cannot understand the manufacturers stating cable size either as they cannot know the installation methods although you do say minimum... even taking into account rheostat control if its completely possible that you can have most of the loads on then the cable must be protected however rare these occasions are - you may choose to do this with the front end device but I'd rather not be called out on xmas day because the whole family is arround and the oven/hob are in high demand.


Yep the xmas dinner line :) ... ps I'll admit it isn't often but I live in a clicky small town and everyone knows everyone, I have been contacted twice on xmas day for this very reason albeit twice over 20yrs -it does occur.
 
Last edited:

Reply to Hob and oven single supply cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
966
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock