Discuss Horse Stables and Workshop in the UK Electrical Forum area at ElectriciansForums.net

I for one can tell you that E54 is spot on with his advice when it comes to the sub main !
I will hopefully soon to be reporting back on another thread as to the out come of a fault on a largish sub main we have been tasked to sort out which appears not have been laid correctly and it does somewhat look ominous at the moment .:disappointed:
 
Hi Guys,

Thanks so much so far for all the feed back so far.

In answer to a few points raised, yes I'm a sparks but I very rarely do any installs now and certainly never been involved with agricultural / horticultural installs as for the last 25 years I have been involved in maintenance and fault finding mainly, so I want advice from people who have experience in this field (excuse the pun).

It is a freebie job because he's family and we're close, I can also rely on him to help me out whenever / whatever I need.

The submain has been laid in soft sand at a depth of 1000mm, cable warning tape was laid on top of the sand before trench was back filled.

Regards,

ruu
 
I have worked on a few stables over the years
a few practical things to bear in mind
Rats like being near horses and horses bedding and food
so I always used metal conduit or SWA
horses wee is corrosive !
just want to throw that in
horses seem to have a nasty habit of dropping dead when in receipt of very small voltages
had a problem on a job ( not of my doing) a vet called me over as the Horse had keeled over brown bread, gradients was the problem and the earth electrode was adjacent to the building so a small voltage was detected a few feet away, usualy they recomend earth electrodes to be some distance from the building
any thing electrical switch gear sockets etc in stables needs to be substantial as for some odd reason horsey people are a trifle clumsy and often a little intoxicated !
i have often found in that in conversation horses are more intelligent than their owners !
sorry I cant be of much technical help just thought I would throw a few words in
ps consider an alarm as well as tack room thefts are regular
 
Last edited:
and with intruder and fire alarm sounders,put them outside of the building not inside the stable block,a spooked horse is a dangerous beast..
 
As Phil D said, all lighting runs on top beam, but switches (IP rated) between each stall, far enough away from any inquisitive horses. Sockets in tack room; if power needed, then use an extension lead.
 
you dont want an extension lead running through a stable block,bar the trip hazards a cable possibly running through water and the potenial for a horse just to stand on it and crush it adds other risks,an external socket would be best to provide power for the vet and blacksmith.
 

Reply to Horse Stables and Workshop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
669
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock