There are specific circumstances where you cannot use Tncs (like caravan parks I believe, it has to be rodded, as a fellow forum member I know who works alot for the Caravan Club will testify).


Is a hot tub one of these instances?

The only other problem is with services like water pipes - which means main bonds also need to be extended- which could be a pain.


Apart from that I 'd rather have a Zs of 0.3 than 37 or 17 or 7 .....?
 
Unless there's a specific reason, why can't you export it?

The Dno's dont approve of extending their PME earth beyond the equipotential zone of the building in which the supply is located.
This is only an issue if there is exposed / extraneous metalwork at or around the hot tub ,
as in the unlikely event of a neutral break this metalwork may rise to a dangerous potential.
hope this helps.
 
I replied in the other thread, I installed my tub using the supplied tncs earthing arrangement also putting a rod in at the tub end. This rod was well below 22 ohms as stated in the regs, the only problem I had was when you got out the tub and one leg was on the floor and one in the water you could feel a shocking feeling, slight difference between true earth and suppliers earth, therefor I disconnected the suppliers earthing and made the tub tt. Alls fine now so that's how I install them from now on!
 
There are specific circumstances where you cannot use Tncs (like caravan parks I believe, it has to be rodded, as a fellow forum member I know who works alot for the Caravan Club will testify).


Is a hot tub one of these instances?

The only other problem is with services like water pipes - which means main bonds also need to be extended- which could be a pain.
agreed , so in that instance you have a choice of running a 10mm earth bond from the MET to the outside pipes or , bang in earth rod near hot tub.
most choose the earth rod method if its a long run back inside and they're only using a 6mm cable anyway.



Apart from that I 'd rather have a Zs of 0.3 than 37 or 17 or 7 .....?
so would i lol

.......................
 
But if you export and have rcd protection how can people feel the tingle when getting in and out. This must be potential difference with the value at the met(via tncs) and the ground where the tub is located, part of body in the water and foot on the ground. Surely the max difference would be 50v any more the rcd would trip
 
cheers for that 'keithsims' ................... NO exposed metalwork etc at the hot tub but I think if you TT it and the readings are good then this is the way to go.
 
last hot tub i did was off TNS , didnt bother with any rods :-D

If the hot tub was located on bare ground or grass, i think i'd be also installing a rod, even if it was a TN-S supplied installation. Your still going to get a potential difference between true earth and the DNO TN-S earth.....

As for the Regs, i think they state somewhere, that a TNC-S supply can be used, for supplying hot-tubs and the like provided an earth electrode of a certain value is also provided.... I think that value was around 20 ohms, but i wouldn't swear to it...
 
How many lost neutrals have you seen? And how long before fixed.

Me-none.

Knackered RCDs owner unaware of, prob been like it since installation by a (*cough*) electrician?

Me-about 15.
 
I think earlier posters were trying to decide on TNCS or TT. E54 you're proposing TNCS with a back up rod as well aren't you. All connected together, so to speak.
 

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
571
I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock