Its not just about a fault on the tub, you should TT a hot tub, its all about the potential difference between true earth and the MET (PME)

Its the failure of the PME thats the worry here,

Why? because 1 in ten million have temporarily lost the neutral that is subsequently fixed pronto?

Plus class 1 fittings in and around the tub could be a problem.

personally i would TT a hot tub

So you prefer to rely on a device thats proven to be unreliable and subject to high failure rates (the RCD) for disconnection! Theres a lot more chance (probably several orders higher) of the RCD failing than the PME neutral being lost.


Don't get me wrong I am not a fan of PME (TNS all the way) but .... the logic puzzles me. Loss of neutral is unheard of. And fixed quickly the miniscule few times it happens. RCD failure is rife and often never checked, fixed or found. Especially when they're fitted by a "friend" that has 'acquired' the board and RCD and has no registration, invoice, and more importantly, test equipment. Changed a few things for a mate who had the board changed 8 years ago, as above, RCD was kaputt. Probably never worked. How would we know? It was never tested.
 
Last edited by a moderator:
So you prefer to rely on a device thats proven to be unreliable and subject to high failure rates (the RCD) for disconnection! Theres a lot more chance (probably several orders higher) of the RCD failing than the PME neutral being lost.


Don't get me wrong I am not a fan of PME (TNS all the way) but .... the logic puzzles me. Loss of neutral is unheard of. And fixed quickly the miniscule few times it happens. RCD failure is rife and often never checked, fixed or found. Especially when they're fitted by a "friend" that has 'acquired' the board and RCD and has no registration, invoice, and more importantly, test equipment. Changed a few things for a mate who had the board changed 8 years ago, as above, RCD was kaputt. Probably never worked. How would we know? It was never tested.

How would you know if the Earth was lost on a TN-S? That's one advantage of PME, the DNO are alerted to it.

Each system come's with risk, non are infallible.

Broken PEN'S, it hapens, quite rare

RCD'S failing, it happens, more down to not testing the RCD quarterly or the system to which it connects to than the RCD itself.

TN-S loss of Earth, it happens, though very little TN-S in most area's now, certainly Domestic anyhow.
 
Hi Chr!s

good point re loss of earth on TNS. Not sure. Assume most losses would be because cable is severed or damaged, isn't the outer usually the earth on TNS?

I'm just a cynic and suspect they dropped the idea of having 3 hard lines back to the sub station as it is (clearly) cheaper to have 2 instead.... all about money.

I agree, nothing is infallible.

Not sure about the quarterly testing. I have come across a few that operate satisfactorily on the test button, but do not operate when tested (ramp, x1, etc) and have been replaced). So as mentioned, nothing is infallible including the test button!

TNS a dying breed.

Don't know much about the construction, etc between a house and substation of a TNS cable. Would love to though!:D
 
Don't know much about the construction, etc between a house and substation of a TNS cable. Would love to though!:D

Here you go!
View attachment 14514
1/ Outer sheath (PVC)
2/ Armouring
3/ Bedding
4/ Sheath (lead or lead alloy)
5/ Fabric tape
6/ Worming (filler)
8/ Insulation
10/ Conductor
The picture is of a MV cable so I've missed some bits out that aren't used for LV
 
New posts

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
678
I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock