    Im relatively freshly qualified and registered so still coming up against new challenges.

    I have a client who has requested a rewire but they also want minimum damage to flooring etc. Hopefully loft access means I can get to first floor lighting cables but ground floor ceiling lighting could be tricky.

    Provided testing on current cabling comes within correct values is it okay to reuse??

    Also, whilst sticking with safe zones is it acceptable to chase around corners, I presume as my chasing tool won't get right into the corners a chisel will have to do the tight spot?

    As a side note, install has every variety of back box surface mounted even with big fat finger holes, L/N reversed, sockets with no Earth, trailing cables in front of doors no main earth supply - otherwise its perfect!!!
     
  2. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    A difficult job then, I would suggest you tell your client he needs a EICR prior to any rewire, with the state if the wiring that you have mentioned, a complete rewire is required not just the lighting, is the bonding OK? what about RCD protection as you are chasing in all the cabling?
     
  3. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    From what you describe it don't sound great. It would be difficult to say from a distance whether the existing lighting cables are okay, you need to test it and give it a thorough inspection but if the power circuits are how you describe, the lighting may well be the same.
     
  4. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    As others have said get the test gear out first and do a full periodic. It may end up being a full rewire but equally if a few results come back good you could save the customer a few shillings.
    If you're new to periodic testing which it sound like you may be it might be an idea to enlist the help of an experienced Tester.
    Good luck either way.
     
  5. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    If new cable needs to be provided, so be it, we can not magic them in.If he knew the wiring was in such a state?,why finish the decoration.?
     
    • Like Like x 2
  6. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    The customer seems to have made the strategic decision to have a 'rewire', probably based on a visual inspection and the age of the property, one assumes you've come to the same decision on the same basis. Unless you are going to do the EICR for free, why waste £200 of the customers money, when they want it 'rewired'?

    If you going to 'rewire', then it's floors up or ceilings down. If I was paying for a 'rewire', I would not want any of the old cables used, unless they were very recent additions.
     
    • Like Like x 2
  7. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    Absolutely, the customer will have to way up the cost, either floor up, or ceilings, maybe not all down, negotiating joist runs switch drops etc, it can be done, but time will have to be spent to minimize damage , which means more labour time.
     
    • Like Like x 1
  8. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    You could always use those new fangled Wi-Fi sockets :)
     
  9. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    From my experience if the power is that bad the lighting is probably worse.
     
  10. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    Thanks for all the advice.

    The plan was to do a complete rewire from the CCU upwards. There doesn't even seem to be a supply earth so power distributor coming out to rectify that then energy supplier fitting a main isolater switch before I begin.

    I was going to suggest to the client that I could surface trunk cables to lighting roses if they really don't want any flooring or ceiling disturbed but that seems like a poor finish in my book.

    Photo shows current fuseboard and supply etc. Far right of picture has a small terminal with three earth leads - one to fuseboard, one to bonding and one really long one that attaches to a water pipe, but nothing from supply.

    Fortunately, the property isn't being lived in. I've advised the client of all the current failings with photos.

    IMG_5852.JPG
     
    • Useful Useful x 1
  11. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I have only used trunking where access to the cavity above the ceiling is not possible, in your case it is.
     
  12. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    There is a loft hatch on the first floor but I've not gone up to check access. My main problem is they don't want the floor on the first floor removed.
     
  13. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    What flooring is down that they don't want lifting ?
     
  14. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    Its all fairly new laminated flooring by the looks.

    IMG_5845.JPG
     
  15. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Ugh. Make sure they are aware of the significant increase in cost and time due to the floor not being able to be lifted to facilitate the rewire, as well as the increased plastering needed to repair chased walls.
     
  16. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    Definately... I'm guessing the chance of being able to pull through the old cables through where the ceiling rose is will probably be a complete no hope...
     
  17. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Ah that's a problem. Tell them laminate is old hat.
     
  18. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    If you manage to pull them through buy a Lottery ticket, I wouldn't even try.
     
    • Like Like x 3
  19. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    Yeah, I figured as much... I'm going to make sure they are fully aware of whats involved. And explained what chasing is I suppose.

    Its the first time I've used this forum and it has proven very helpful. Thanks all..
     
  20. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    No worries.
     
  21. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    That laminate looks carp, starting to blow already. Have your clients any ideas of what a 'rewire' entails? Trying to pull cables via the ceiling rose hole is one thing, how are you going to do the switch drops, sockets etc without having some of the floor or ceiling down?
     
  22. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    I tried to persuade them to go surface with trunking, I think they may be renting it.

    I may show them photos of what chased walls look like.

    If I chase up from the switches what is the best way to bring the cables out to trunk along the ceiling? Would a sunken flex outlet box with the cable troubled along the ceiling meet with Regs? Not the best looking solution but if I can access above ceilings or below floors.
     
  23. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    What about suggesting having coving put up. you could clip the cables round or use bases and ties as there be within the 150mm zone where the wall/ceiling meet. could cut holes to fish cable across to light position which will all be covered by the coving. A bit of faffing about but achievable just leaves the chases for the switch drops.
     
    • Like Like x 1
  24. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You could use architrave trunking, keep the switches surface and bring the trunking up beside the door frames. It is in inevitable that the trunking will cross the ceiling to the lighting point. How are you doing the power on the ground floor.
     
    • Like Like x 1
  25. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
     
  26. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    By architrave trunking do you mean like the D-line curved stuff? Not a bad idea. How do I go from trunking to ceiling. I was thinking perhaps a slotted disc of mdf or is there a product for this?

    As for power I think I'm alright with that. Incoming supply is in basement so I was planning on bringing up behind the skirting then chasing up to first socket and horizontally to others.

    For ground floor power circuit of two rooms and hallway so 5 dbl and 1 sngl socket I was hoping a radial would do?
     
  27. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Ceiling Rose Base Adaptor for MT1 + MT2 Trunking | QVS Electrical Wholesalers - http://www.qvsdirect.com/ceiling-rose-base-adaptor-for-mt1-mt2-trunking
     
  28. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
  29. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Remember if your going to use trunking across the ceiling you may have to use D line clips, elsie fixings or a similar product within the trunking if it forms part of an escape route.
     
  30. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt

    Thank you. I will beat that in mind.

    Am I right in saying that as part of a rewire I also need to include smoke, heat and CO2 detectors. And these should be on a separate circuit?
     
  31. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you don't have to fit these detectors, but it's good practice to do so. they can be on their own circuit or on a frequently used lighting circuit, your choice.
     
  32. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt
    It randomly has a small fuse box on the first floor serving the upstairs lighst and sockets. I'm guessing it used to be a HMO house.

    IMG_0892.JPG
     
  33. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
     
  34. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Not having luck with replying with quotes! In case it's not obvious; If they are renting, have you checked with the landlord?
     
  35. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    Are you clicking reply or quote mate, cause I am sure if you hit reply it comes back the way your's did but if you hit quote and insert quote it comes back like this one.
     
  36. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I just hit reply and type :)
     
    • Like Like x 1
  37. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    I've just replied to mine.
     
  38. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    Ok so we've just proven you need to hit quote instead of reply, another happy customer and it's not even 9am.
     
    • Like Like x 1
  39. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    This is reply :)
     
  40. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    This is quote :) Hang on, I ain't got 'Quote' just '+Quote'
     
    • Like Like x 1
  41. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    Yeah sorry Mid, You hit +quote then hit insert quote under the text box which then opens a box with your quotes in and hit insert these quotes.
     
  42. GMES
    Offline

    GMES Chief Gorilla Staff Member Trusted Advisor

    Public announcement!!
    No boxes were injured during all that hitting of boxes:eek::eek:
     
    • Like Like x 1
  43. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Cheers. Blooming fudgy fingers :oops:
     
    • Like Like x 1
  44. Diddy
    Offline

    Diddy Regular EF Member

    Mini Trunking across the ceiling....yuk lol. Why can't you mini trunk to ceiling and then fish across ceiling ? Consider feeding switches and taking SW+N from Switch to fitting.....Or even a 3 core in the event you need a feed at light for say a fan connection or to tap off for smoke detectors or whatever. Even if you are super unlucky and the route from switch to light is across the joists you can cut out ceiling at each joist drill joists using angle drill and stumpy wood bit feed cables through and then repair ceiling. Repairing ceiling wont be too hard - Just replace each nicely cut out piece of ceiling back where it was with some little pieces of 2"x1" wooden noggins above to screw the pieces back in place. a bit of finishing plaster, rub it down after it dries - bit more plaster, rub it down again.....Job done - ceilings would need repainted by A N Other.....As above adjust your quote to reflect the extra time for patching and filling.
     
    • Like Like x 1
  45. Chrisknowlesuk
    Offline

    Chrisknowlesuk EF Member

    Location:
    Cheshunt

    Good idea to feed switches. You're right the mini trunking across ceiling isn't ideal. Its an awkward job. I'm not confident in my finishing skills if I try and fish across the ceiling and make good any holes. I've advised the customer that there will be decorative damage and that they need to arrange someone else to redecorate. Most walls are textured paper that is painted on top
     