domestic house call out today- upstairs lights not working , loop in system looks like bathroom lights is first on circuit , got power leaving breaker but no power anywhere upstairs ,no power at any light or switch.

although the stupid volt pen was flashing on initial contact of some of the circuit clarified with fluke it had no power .

after clarifying no power at any accessories i went into loft to examine routes but loft is mayhem advised for loft clear out before proceeding with fault find

anyone any ideas

breaker not tripping , break in cable somewhere
 
Drop all switches and check then accessories (light fittings) before diving into loft sounds like loose, broken wire also ask if they have changed anything like switches wont believe how much time ive wasted because owner didnt want to admit its their own fault.
 
I would do do r1 rn test go to the board and turn off mcb then connect live and neutral in the board then go to last light on the circuit and test r1 and rn then work your way back till you get a reading that will tell you inbetween what light the break is at
 
Did u ask when they first noticed, had they done anything unusual that day e.g. Been in loft and possibly caught foot on cable without noticing pulling it out of light. Or had they had any work done by another tradesman or DIY and possibly damaged cable somehow that way?
 
asked all usual questions nothing done in house
been like this since sat
mcb defo ok used fluke and showed L-n - L-E on load side
asked when last were in loft and they said xmas
 
defo is the bathroom , as it has 4 cables in loop in all rest have 2
the 4 in bathroom are the normal 1 in 1 out , 1 to switch and theres a fan with timer off it also

- - - Updated - - -

mice in the loft?

i was thinking this , breaker not tripping though so must be through the live only
 
Thats what I was just thinking philD. Junction box in loft with a loose neutral connection been sizzling away for a while and finally snapped??? Should still have 230v L-E though if this happened, just no lights!
 
When you said the voltstick lit but meter read no voltage are you sure its not dropped the neutral?

when testing with the pen it showed it was dead but now n then it would initialy light up on contact then go out straight away done this about 5 times , but fluke showed defo dead

- - - Updated - - -

Thats what I was just thinking philD. Junction box in loft with a loose neutral connection been sizzling away for a while and finally snapped??? Should still have 230v L-E though if this happened, just no lights!

wont be junction box with loop in
 
u meaning bell them out

I'd be doing R1 + R2 on all 3 cores in pairs and comparing the readings.

Just this morning I fixed a wall light for a client. The lights fuse went bang. A cable inside the fitting had broken and estalblished this by taking it off the wall and doing the basics! How the cable got damaged is beyond me, as it was totally encased in a metal fitting!
 
I'd be doing R1 + R2 on all 3 cores in pairs and comparing the readings.

Just this morning I fixed a wall light for a client. The lights fuse went bang. A cable inside the fitting had broken and estalblished this by taking it off the wall and doing the basics! How the cable got damaged is beyond me, as it was totally encased in a metal fitting!

i take on board what your saying but theres lne leaving board and nothing at any of the looped in lights
 
Its not rocket science. With a continuity tester test for you break.. R1+R2 or R1 + RN and RN +R2. surley that should confirm what the break is. After which Is correcting..

I fail to see what you a struggling with bud

lol i know how to carry out continuity test , fair enough i have not confirmed cont for nuetral and earth or live DEAD
but the fact there isnt a live connection at first light tells me its a break somewhere,
bearing in mind i got this call at 4:30pm today spent 40mins casing it out checking for power etc , before going into loft to look above first light to see if there is anything obvious like a fried mouse ,
loft was chocka couldnt see a decimal of insulation
 
If this is a wind up then seriously do one.. Had enough over the last day or so of these idiots..

If its genuine.. Take the advice that everyone has given you and test with a proper tester to determine is you have a break and if so what are and where it is.

Sounds like this guy is paying top dollar for you to turn up and determine a fault with only a volt stick...

If you were working on my house id be pretty peed off if you turned up and either 1) didnt have the relevent test gear to test or B) know how to use it to fault find..

Either take the advice or disappear to screwfix forum
 
If this is a wind up then seriously do one.. Had enough over the last day or so of these idiots..

If its genuine.. Take the advice that everyone has given you and test with a proper tester to determine is you have a break and if so what are and where it is.

Sounds like this guy is paying top dollar for you to turn up and determine a fault with only a volt stick...

If you were working on my house id be pretty peed off if you turned up and either 1) didnt have the relevent test gear to test or B) know how to use it to fault find..

Either take the advice or disappear to screwfix forum

take a breathe , i could see your point if a came on and said cant find voltage im stumped
only said at this stage no power at any accessory ,clarified 1st light NO ACCESS TO LOFT ,wasnt wasting any time dead testing when i cant even get in loft to trace the fault
 
ORIGINAL POST---------------domestic house call out today- upstairs lights not working , loop in system looks like bathroom lights is first on circuit , got power leaving breaker but no power anywhere upstairs ,no power at any light or switch.
although the stupid volt pen was flashing on initial contact of some of the circuit clarified with fluke it had no power .
after clarifying no power at any accessories i went into loft to examine routes but loft is mayhem advised for loft clear out before proceeding with fault find anyone any ideas ,breaker not tripping , break in cable somewhere,

NOTICE I ASKED ANYONE ANY IDEAS , THIS WAS MEARLY A BRAIN WORKING EXERCISE NOT HELP/SOS SPARK WITH VOLT PEN CANT FAULT FIND

jeeeez
 
No,jeeeez, this is an ELECTRICIANS FORUM you would have crucified a DIY'R for this, BASIC fault finding mate Basic :wub:

round in circles m8, i didnt say i gave up and didnt know what to do next , clearly explained in op what i had done and that access prevented further investigation
point of post was for some ideas solely for the fun of it
and you guys all jump at the chance to crucify anyone
 
I skipped page 2 as boring, but I go to a lot of faults of all shapes and sizes in all different installations, it's very rare you just get a leg go "down" it's normally a loose connection or something someone has done, if they haven't done anything I'd be checking connections before ripping loft to bits. I get your post wasn't a cry for help as such and I think people have jumped on you a tad unfairly here so I think it's time to quit this one and you can tell everyone what you found tomorrow and give them the V sign if you was right. :hurray:
 
make sure the bathroom is the first light, confirm this by testing all the 3 cores, and if nothing there try each fitting testing continuity,
if no reading at all this will confirm 1, 2 or all 3 cores are broke to first light.
then u could dissconnect the lne out of the db and wire a temp link to first light , put power on they then should all work. then carry out all relevent tests after repair
 
I skipped page 2 as boring, but I go to a lot of faults of all shapes and sizes in all different installations, it's very rare you just get a leg go "down" it's normally a loose connection or something someone has done, if they haven't done anything I'd be checking connections before ripping loft to bits. I get your post wasn't a cry for help as such and I think people have jumped on you a tad unfairly here so I think it's time to quit this one and you can tell everyone what you found tomorrow and give them the V sign if you was right. :hurray:

cheers onions :hurray: glad someones not been on the fighting juice ,
will clarify there are no hidden joints anywhere in loft and check all connections , really dont think the L will be down will be a loose connection from where it leaves board upto loft
 

Reply to HOUSE upstairs lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
707
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
777
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
987
We are having issues with our electrical system. In the garage, dining room, kitchen, one of two bathrooms, master bedroom and the front yard...
Replies
5
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top