  1. mikemolo70
    Offline

    mikemolo70 EF Member

    Location:
    Manchester
    i ask this because i want to run a spur off a socket, the socket is a single and it has 6 cables in so i am presuming it is on the ring main but i was wondering if its a spur and another spur has been run off it, it will also have 6 cables in it so how do i tell the difference.

    thanks for any advice offered.
     
  2. Andy78
    Offline

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    Hi Mike, are you an electrician ?
     
  3. mikemolo70
    Offline

    mikemolo70 EF Member

    Location:
    Manchester
    no i'm not mate have done 2 years at college learning the basics so i can do a few little bits, i don't get carried away with myself though electricity is not to be taken lightly.
     
  4. Andy78
    Offline

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    Do you have the testing equipment and knowledge to be able to test this alteration to verify safety in accordance with BS7671 once you have completed it ?
     
  5. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Do you mean 6 wires 2 Lives 2 Neutrals and 2 earths?
     
  6. mikemolo70
    Offline

    mikemolo70 EF Member

    Location:
    Manchester
    yes thats what it is
     
  7. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Only using a tester can you really establish the facts
     
  8. saspm
    Offline

    saspm Guest

    What size circuit breaker is on the socket circuit you are working on? if it is 16amp or 20amp then you don't have a problem adding to this radial circuit with 2.5mm cable. If it is run from a 32amp you need to do a R1 + R2 test. Best left to an Electrician if unsure and no test equipment!
     
  9. mikemolo70
    Offline

    mikemolo70 EF Member

    Location:
    Manchester
    its a 32amp circuit breaker i won't be touching it until i'm sure anyway i know a little about electrics but not enough to just go adding things without being certain it's going to be safe thanks
     
  10. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    It could just be a down rated RFC with 20 A breaker, a full RFC test is required
     
  11. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    The OP says it's a 32A.
     
  12. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    OK. Break the circuit at the socket in question. Check for continuity between the two line conductors. If continuity is present, it's likely to be on the ring (could be on a figure of 8 loop). To confirm, remove the line conductors at the board. If this removes continuity at the socket, you've confirmed that the socket is on the ring.

    Then do all the usual tests to check the circuit for insulation resistance, Zs, etc.
     
  13. mikemolo70
    Offline

    mikemolo70 EF Member

    Location:
    Manchester
    thanks
     
  14. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Not sure I agree with that 100% - I would check the continuity of the CPC and also make a note of the readings of all 3 conductors....
     
    • Like Like x 1
  15. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Do the correct freakin test fer C---st's sake
     
Loading...
Similar Threads - socket ring spur Forum Date
Adding socket on to kitchen ring-no rcd Electrical Forum Jan 22, 2019
Trying to match Socket outlet. Electrical Forum Friday at 9:27 AM
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. how.to.know.if.a cable is main or spur

    ,
  2. how to test if a socket is on a ring

    ,
  3. how to test if a socket is on the ring

    ,
  4. continuity test spur,
  5. checking if socket is a spur,
  6. tell if a sockect is a spur,
  7. check if socket is off ring main,
  8. ring spur circuit
Electricians Directory Post a Domestic Job Post a Commercial Job