Discuss how do i know if a socket is on the ring or if its a spur off spur in the The Welcome Forum area at ElectriciansForums.net

M

mikemolo70

i ask this because i want to run a spur off a socket, the socket is a single and it has 6 cables in so i am presuming it is on the ring main but i was wondering if its a spur and another spur has been run off it, it will also have 6 cables in it so how do i tell the difference.

thanks for any advice offered.
 
Do you have the testing equipment and knowledge to be able to test this alteration to verify safety in accordance with BS7671 once you have completed it ?
 
i ask this because i want to run a spur off a socket, the socket is a single and it has 6 cables in so i am presuming it is on the ring main but i was wondering if its a spur and another spur has been run off it, it will also have 6 cables in it so how do i tell the difference.

thanks for any advice offered.
Do you mean 6 wires 2 Lives 2 Neutrals and 2 earths?
 
What size circuit breaker is on the socket circuit you are working on? if it is 16amp or 20amp then you don't have a problem adding to this radial circuit with 2.5mm cable. If it is run from a 32amp you need to do a R1 + R2 test. Best left to an Electrician if unsure and no test equipment!
 
What size circuit breaker is on the socket circuit you are working on? if it is 16amp or 20amp then you don't have a problem adding to this radial circuit with 2.5mm cable. If it is run from a 32amp you need to do a R1 + R2 test. Best left to an Electrician if unsure and no test equipment!
its a 32amp circuit breaker i won't be touching it until i'm sure anyway i know a little about electrics but not enough to just go adding things without being certain it's going to be safe thanks
 
its a 32amp circuit breaker i won't be touching it until i'm sure anyway i know a little about electrics but not enough to just go adding things without being certain it's going to be safe thanks
It could just be a down rated RFC with 20 A breaker, a full RFC test is required
 
OK. Break the circuit at the socket in question. Check for continuity between the two line conductors. If continuity is present, it's likely to be on the ring (could be on a figure of 8 loop). To confirm, remove the line conductors at the board. If this removes continuity at the socket, you've confirmed that the socket is on the ring.

Then do all the usual tests to check the circuit for insulation resistance, Zs, etc.
 
OK. Break the circuit at the socket in question. Check for continuity between the two line conductors. If continuity is present, it's likely to be on the ring (could be on a figure of 8 loop). To confirm, remove the line conductors at the board. If this removes continuity at the socket, you've confirmed that the socket is on the ring.

Then do all the usual tests to check the circuit for insulation resistance, Zs, etc.
thanks
 
OK. Break the circuit at the socket in question. Check for continuity between the two line conductors. If continuity is present, it's likely to be on the ring (could be on a figure of 8 loop). To confirm, remove the line conductors at the board. If this removes continuity at the socket, you've confirmed that the socket is on the ring.

Then do all the usual tests to check the circuit for insulation resistance, Zs, etc.

Not sure I agree with that 100% - I would check the continuity of the CPC and also make a note of the readings of all 3 conductors....
 
turn off MCB. take one of the L conductors out of the MCB. turn MCB on. stick finger on the end you have took out. if it bites, it's a ring... sssimplesss. :mad:
 

Reply to how do i know if a socket is on the ring or if its a spur off spur in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
713
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
716
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
244
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
769
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock