Tbf I would’ve paid more…but I got 3 quotes, 2 being £3500 & the third was this fella who said he could get it done in a day for £3150 - said he puts all his lads on it which is why he can get it done so quickly - but thought this was around the right price with 3 people quoting it.
No RCD trip times but all the test buttons operate???
No IR results.
Arc fault protection on EVERY circuit.
That certificate is as dodgy as the wiring.
 
Short circuit capacity of supply fuse 100KA.
seems like a made up number to me!
I am suspicious about some of the other test results, they seem to good to be true.
 
No RCD trip times but all the test buttons operate???
No IR results.
Arc fault protection on EVERY circuit.
That certificate is as dodgy as the wiring.
Obviously my electrical knowledge is minimal so I just assumed everything was right - I’ve had a plasterer in already 🤦🏽‍♂️ Is there a way to test everything rather than having to rip everything out again?
 
Exactly what I thought when reading the OP and wondered if they work in the north of England?
The 1 day Re-wire guy from Scotland him and his team appeared to do work to a reasonable standard , a bit rough when it came to chasing out walls but I don;t remember seeing him bury connector strip in the walls and under the skirting boards

The 1 day re-wire in this thread looks like it was done by people who just didn;t give damn
 
New posts

Reply to How not to standard is this rewire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
859
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
868
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
871
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
422

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock