I'd tear the circuit apart and ring out each wire run with a long lead to see what is joined to what then sketch it out and make sure I am happy with it, I then rip up the floor if needed or downrate the circuit if neccessary.
 
thought it was only plumbers that ripped up floors.
 
I have found some thing under those floors that others have chosen to ignore.

Taped joints, JB spider webs on 32A OPDs, unenclosed connections, rodent damaged cables.

But don't worry I always poke the camara down there first to see if there is a real need to rip up the floor. If there is - it is better than a fire...
 
I have found some thing under those floors that others have chosen to ignore.

Taped joints, JB spider webs on 32A OPDs, unenclosed connections, rodent damaged cables.

But don't worry I always poke the camara down there first to see if there is a real need to rip up the floor. If there is - it is better than a fire...

...Was it you,that took 6 months to do that EICR on that womens' prison shower block? :bobby:
 
Of course if your DIY it wont matter because as we all know.
They spur from a spur all the time, and 10 years down the road have never had a problem.
Why ??
Because kitchens aside, the loading on that extra bit of 2.5 is never likely to exceed its rating.
Did I just say that on an electricians forum ????
Spank me somebody pleeeese !!! :icon12:
 
...Oh the memories...remember watching that soapy-drivel,at me nans as a kid...My youngest has a pal whose mum works in a womens prison,and it sounds a VERY worrying task :bobby:
 
...Oh the memories...remember watching that soapy-drivel,at me nans as a kid...My youngest has a pal whose mum works in a womens prison,and it sounds a VERY worrying task :bobby:

It ran for so long that eventually we were seeing the same actors playing different roles as the series went on!!
 

Reply to How to tell if socket is on ring or spur off spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
683
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock