Discuss How to tell if socket is on ring or spur off spur in the UK Electrical Forum area at ElectriciansForums.net

bleach

-
Reaction score
0
Ok so you have the classic to cables in back of socket. Spurs should be identifiable through higher resistance but if very short spurs and it's an older install and you want to break into the ring to add another socket. You could be creating a spur off spur off spur?

How do u go about being certain in this scenario before the addition and do u always do it in practice?
 
Ok so you have the classic to cables in back of socket. Spurs should be identifiable through higher resistance but if very short spurs and it's an older install and you want to break into the ring to add another socket. You could be creating a spur off spur off spur?

How do u go about being certain in this scenario before the addition and do u always do it in practice?
Test the continuity of the the Ring Final r1,r2,rn, (R1+R2)
 
if you have 2 cables in a socket outlet, split them then test from 1 to the other for continuity. ( best done with power isolated :ack2: )
 
Sorry guys all posts spot on. Thanks Murdoch sorry if I implied wrongly. My apologies. Happy days :)

My 2nd post is really valid. I was fault finding a "ring" a few weeks back, which at a socket "looked" like a ring and tested as a ring BUT at the CU it turned out to be 1 x radial and 1 x lollipop - on a 32A breaker.
 
Definitely valid. Lollipop snares!!! Cheers. I started this thread to highlight to my buddy these issues which have panned out lovely so thanks again all I hope others may find this of use who stumble across it.
 
Isolate the circuit and connect phase and cpc (R1 + R2) of cable 1 together and do the same to cable 2. At your socket you should have 2 cables with continuity between R1 + R2. Still worth checking the whole circuit out though, R1, RN, R2, R1 + RN and R1 + R2. Best not to use a plug in test lead on old sockets as loose contacts etc can throw the readings out, drop the fronts and take the readings from the screw terminals.
 
I'd tear the circuit apart and ring out each wire run with a long lead to see what is joined to what then sketch it out and make sure I am happy with it, I then rip up the floor if needed or downrate the circuit if neccessary.
 
thought it was only plumbers that ripped up floors.
 
I have found some thing under those floors that others have chosen to ignore.

Taped joints, JB spider webs on 32A OPDs, unenclosed connections, rodent damaged cables.

But don't worry I always poke the camara down there first to see if there is a real need to rip up the floor. If there is - it is better than a fire...
 
I have found some thing under those floors that others have chosen to ignore.

Taped joints, JB spider webs on 32A OPDs, unenclosed connections, rodent damaged cables.

But don't worry I always poke the camara down there first to see if there is a real need to rip up the floor. If there is - it is better than a fire...

...Was it you,that took 6 months to do that EICR on that womens' prison shower block? :bobby:
 
Of course if your DIY it wont matter because as we all know.
They spur from a spur all the time, and 10 years down the road have never had a problem.
Why ??
Because kitchens aside, the loading on that extra bit of 2.5 is never likely to exceed its rating.
Did I just say that on an electricians forum ????
Spank me somebody pleeeese !!! :icon12:
 
...Oh the memories...remember watching that soapy-drivel,at me nans as a kid...My youngest has a pal whose mum works in a womens prison,and it sounds a VERY worrying task :bobby:
 
...Oh the memories...remember watching that soapy-drivel,at me nans as a kid...My youngest has a pal whose mum works in a womens prison,and it sounds a VERY worrying task :bobby:

It ran for so long that eventually we were seeing the same actors playing different roles as the series went on!!
 

Reply to How to tell if socket is on ring or spur off spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
789
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
807
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock