I am working on a property refurb where there is a new hot water system to be put in place. The hot water is to be stored in a cylinder located in the hallway. The hot water is to be heated by a combi boiler but there are also 2 x immersions in this large tank, one at the bottom and 1 x halfway up in case the combi fails.
These immersions are 3 kW each. I was just wondering what you guys reckon is the best method of control for these? Cable size wise I was thinking of running a 6mm to a control switch where I would then branch off to each immersion with a 2.5
Do you think I should just use a standard on/off switch (rated 25A plus) or have two seperate switches or even a programmer type control with one immersion being a boost
would run 2 16A circuits in 2.5 mm (seems overkill as they will possibly never be used)
the highest placed i/htr in the cylinder would be used as a boost
the lowest placed i/htr would be used for for a full tank of hot water
these would only be used in emergency if combi fails so possibly only wire in 1 i/htr
on one circuit whichever one suits best
Maybe a visit to the plumbersforum might shed some light on it....but don't go alone, take a few of the more burly sparks with you to watch your back especially after dark .
Hmm. The whole point about a combi is that the domestic hot water heating is instantaneous, so no need for a cylinder.
I guess, in the end, it doesn't really matter about the detail if the immersion heaters are just for backup in the event of boiler failure; if it doesn't work, it's down to the designer of the heating system, who should tell you what controls are required, if any.
Would guess that the boiler is a system boiler (wired as a s plan or y plan) and not a combi, would not be able to use a combination boiler with a water storage tank.
best to wire 2 x 16A radials in suitably sized cable.
Regarding the 2 Immersion Heaters in the Cylinder that brizospark / the OP asked about:
When a Combi Boiler is installed in a Property that has more than one Bathroom or has a high Hot Water demand - perhaps after a refurbishment or an Extension is built - quite often a Cylinder is installed which is Heated by the Combi via Flow & Return Pipework to the Cylinder Coil and a Zone Valve & Cylinder Thermostat and Timeswitch - the Cylinder would usually supply the Hot Water for a Second Bathroom for example.
Unless the Cylinder in this case is a Large Capacity Cylinder I am surprised to read that it is in a Property that has 5 Bathrooms !
Theoretically even with 28mm Plumbing Pipework a Hot Water Cylinder would only be able to supply 2 X Bathrooms simultaneously - with perhaps the Combi supplying another - only ONE Hot Water draw off is possible from MOST `Average Capacity` Combi`s.
Although with a High Capacity Combi the Manufacturers state that 2 Hot Water draw offs are attainable - dependant on the correct Volume of Water Mains being available and other factors relating to the Hot Water system pipework resistance factors - and the correct Volume and pressure of Gas available at the Combi.
I realise that in this case the Family members might all have their own Bathrooms which are all normally used at different times [?] - BUT I am fairly sure that there would not be more than 2 Bathrooms connected to the Combi even if it is a High Capacity model - ?
It IS obviously possible depending upon the Lifestyle of the Family that the Combi could heat the Cylinder to meet the Hot Water requirements of a 5 Bathroom Home in conjunction with the Instant Hot Water from the Combi - BUT - Personally I am very sceptical of that.
Obviously I have written these details knowing nothing more about the Property or the People who live there than I have read here.
I would definitely suggest that the OP wires these 2 Immersion Heaters as if they will BOTH be being used DAILY - and possibly for long periods of time - depending on the Hot Water usage in this 5 Bathroom Home.
Even IF the Immersion Heaters are NOT going to be used as regularly as I am GUESSING here - what about if another Family purchase the House in the future and their Hot Water requirements are totally different from the existing owners - meaning that they do have the Immersion Heaters On Daily for Hours at a time - ? I realise that there is no suggestion of the Immersion Heaters being wired in an unsafe manner - but would there be different requirements [apart from Timed operation] for the Electrical Installation for 2 Immersion Heaters that are used on a Daily basis for Hours at a time - ?
I am NOT trying to complicate this Electrical Installation for brizospark / the OP - but I would be guessing that these 2 Immersion Heaters will be getting far more use that the Plumber suggested to Him - ?
Regards,
Chris
Last edited:
Reply to HW Cylinder - 2 x immersions in the UK Electrical Forum area at ElectriciansForums.net
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical
forum online. General electrical questions and answers can be found in the electrical forum.
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.