Another Sticky thread.
Discuss I am a new PV householder - advice please. Unbalanced strings and wrong inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Another Sticky thread.
Is it verbar or on a contract ?
Thanks FB - a couple of points. You specifically emphasise your "cool downstairs utility room". Is loft mounting a problem? It does get pretty hot there in the summer... (Standard red/brown concrete tiles)..The inverter and isolators should be clearly labelled, including warning stickers and ideally with schematics provided nearby - here's mine (wall-mounted in a cool downstairs utility room). edit: there is also a "warning: dual supply" yellow sticker on the CU (fusebox).
Thanks FB - a couple of points. You specifically emphasise your "cool downstairs utility room". Is loft mounting a problem? It does get pretty hot there in the summer... (Standard red/brown concrete tiles).
The electrician said that he would not need to replace the consumer unit because he would be able to use one of the "ways". As yet, there is no apparent change to the CU, certainly no new labels on the 3 free ways or anything else. It is possible that this happens with the final connection - certainly the power didn't go down yesterday.
Oh I am following advice - I have an email drafted that clearly tells them to stop - though how I stop the roofer from leaving home on Monday morning at 5:30am to travel 100 miles to us I don't know! Not my problem.You must follow advice and stop the works, it would be futile to carry on as lots of errors have already been made. Did you choose the contractor because of price or were they recommended?
You must think long term on this decision.
Hmmmm....If I was quoted for a BMW and was delivered an Audi I would at least expect an explination
Let them finish it and then ask why???
At least you have working kit and have only paid 25%
your system is not going to work!! correctly if it works at all
I sent a very detailed email and a follow-up text to the sales person and she called me in 5 minutes. They will try to stop the roofer travelling if they can and know that I am er, unhappy, to say the least.... I suspect you may end up not having the four panel array and use a smaller inverter on the remaining 12 modules, at least this setup will do what it says on the tin.
I'm not far from you, if you need advice and it cant be resolved.
There is no way that four Suntech panels will operate the MPPT channel, even if you did mange to get an output now, or managed to reduce input voltage parameters, in 10 years time after degredation it would stop operating anyway, five is almost always the minimum from experience. .............. I suspect you may end up not having the four panel array and use a smaller inverter on the remaining 12 modules, at least this setup will do what it says on the tin.
Thanks FB. This is pretty much where I have got to. My email was civil and factual. I am asking them to come up with a spec for 4 panels into 1 inverter and 12 panels into another inverter. This will cost them more but I expect them to swallow it. It will cost me more since I understand inverters need replacing after 10 years, and I will have to replace 2. I am hoping that prices come down with economies of scale!...
So unless by some miracle the inverter MPPT can cope with a single string of four panels, or unless a 1kW and a 3kW inverter is used in a twin-inverter system, then I see the system being downsized.
I think that the best course of action is not to cancel or to start gobbing-off, but to try to work amicably on an agreeable solution.
There is a tech spec PDF on this page - their quote had said they were using STP245S-20/Wd 245 W (and I have 16 of them in my garage!)What is the voltage of Suntech panels? If they are high voltage like some 12 x 50v = 600v, this will be a problem when the panels get cold as the voltage will spike and possibly blow some models of inverter.
Also the DTI guide has specific requirements for RCD protection, it is unlikely that you can connect it to a spare way in an existing box also you run the risk of having no RCD protection in the event of electrocution, some inverters can take .4s to discharge /power down.
I think you legally need to allow the present installer to rectify the issues to a satisfactory standard, I suggest you hire a local installer (billing the present installer for their time) to oversee the works and ensure the rectifications are completed to at least a minimum standard.