Discuss I am getting very high zs readings in the UK Electrical Forum area at ElectriciansForums.net

banny07

-
Arms
Reaction score
39
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
 
Last edited:
None of those figures make sense to me.

I assume zdb is at the db after measuring ze so should be higher than ze not lower.

How are you doing these tests?

What is the state of the circuit for each test?
 
Last edited:
None of those figures make sense to me.

I assume zdb is at the db after measuring ze so should be higher than ze not lower.

How are you doing these tests?

What is the state of the circuit for each test?
I am teasting ze with main earth disconnected, zdb with earth connected.
 
None of those figures make sense to me.

I assume zdb is at the db after measuring ze so should be higher than ze not lower.

How are you doing these tests?

What is the state of the circuit for each test?
On lighing circuit r1+r2 is 0.86 but zs comes up to 7.66 ohm.on another radial circuit r1+r2 is 0.09 but zs jumps up to 0.52.
 
Formatted slightly differently....
Please note r1, rn and r2, and R1+R2 are different things.
Ze is 0.3 (tns), (OK)
Zs@db is 0.21. (OK - parallel paths I assume)
Ring Final Circuit:
End to End r1 and rn are is 0.42. (OK)
End to End r2 is 0.72 (OK, assuming twin and earth - expected cpc= * 1.67 and is close enough)

R1+ R2 is 0.29 (please use capitals for this - OK - 0.42+0.72 / 4 = 0.28 )

. when I test zs it 8.26 ohm new to testing. NOT OK!

What make and model of MFT do you have?
Are you using different test lead / probe / clip for Zs?
If recent Megger are you selecting 2 wire or 3 wire non-trip Zs?
 
Have you tried a line to neutral loop. I often do this with obscure loops, one it verifies your meter is working and two it verifies the line and if this is okay you could have an earthing issue. With higher than expected loops return to the board and verify your loop at the board again it isn't uncommon for a TN-S system to intermittently break down.
 
Have you tried a line to neutral loop. I often do this with obscure loops, one it verifies your meter is working and two it verifies the line and if this is okay you could have an earthing issue. With higher than expected loops return to the board and verify your loop at the board again it isn't uncommon for a TN-S system to intermittently break down.
R1 and Rn are same on lighting circuit
Formatted slightly differently....
Please note r1, rn and r2, and R1+R2 are different things.


What make and model of MFT do you have?
Are you using different test lead / probe / clip for Zs?
If recent Megger are you selecting 2 wire or 3 wire non-trip Zs?
Megger 1741+ . using plug leads for sockets and using original test leads to test lighting circuit. using 2 low or 3 low leads with same result.
 
Well something is afoot!
I think you need to retrace steps and do several Zs@DB in a row to check results are repeatable, and also double check main earth is properly reconnected.
If the high current loop is working consistently and reliably for the board, there is no reason it shouldn't also work reliably when testing the final circuit with RCBO bypassed.
Try (carefully!) using the exact same probes at the back of a socket to rule out a faulty plug adaptor test lead.

It's plausible that the non-trip Zs is being affected by interference/noise, but the high current should be fine.
(There is a way to use high-current with RCBO's but I won't confuse the issue by talking about that yet.)
 

Reply to I am getting very high zs readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
921
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock