I am teasting ze with main earth disconnected, zdb with earth connected.
Fair enough, although you should be testing for zs using main earth only, removing parallel paths.

Zs can vary a bit even from test to test, but shouldn't be that far out.

You can easily check your mft for correct zs, at home or wherever, measure the zs (say 1. 3 ohm), then measure it again but place a 1 or 2 ohm resistance between your meter leads and the same point, the new zs readings should increase by the value of the resistance you added. (To 3.3 ohm in this example) if it's all OK, them you are measuring something wrong, or you have a poor connection when you reconnected either the circuits, or the main earthing.

There is a possibility of cross voltage from another property, is the bonding correct?
 
I was about to suggest similar to @Julie -
Another thought - if you have a long wander lead with you, measure it's resistance on the continuity range.
Then do Zs@DB again normally. Then Zs@DB with the wander lead between the tester and the CPC bar. It should increase by the resistance first measured.
 
I was about to suggest similar to @Julie -
Another thought - if you have a long wander lead with you, measure it's resistance on the continuity range.
Then do Zs@DB again normally. Then Zs@DB with the wander lead between the tester and the CPC bar. It should increase by the resistance first measured.
I will do this when I go back there. I have another mft (1553) which I will be also using . My concern is how to proceed if It also gives same results.
 
If you do you must go back to the beginning. As @timhoward suggests do repeated Zs at the DB to ensure it is constant then repeat your dead tests.
 
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
 
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
so at the furthest point with all the parallel earth paths removed
by disconnecing main bonding conductors to water and Gas?
 
I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.
There are two reasons to measure ze/zdb , the first is with everything connected I.e. all parallel paths - this will give the maximum fault level, you can then check the protective devices are suitable for that fault level; the second which applies to ze/zdb and zs is with the minimum fault level likely to occur - so at the furthest point with all the parallel earth paths removed, in this case it is to ensure that the protection will operate in the required time in the worst case
No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
 

Reply to I am getting very high zs readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
925
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock