A

amckay

Been to a job today "can you come and have a look at this please my sockets aren't working".
DIY Dave has been in and extended a ring from a point where the client wanted a socket removing.
New sockets now not working. So I proceed to chase around his bodged plastering. This is what I find.
 

Attachments

  • uploadfromtaptalk1416509995239.jpg
    122.3 KB · Views: 207
  • uploadfromtaptalk1416510032972.jpg
    140.7 KB · Views: 184
Yeah its like a wago but made by ideal. I use them myself. I can't believe it, they're rated at 32A and the biggest load connected to the ring was a newly installed electric fire place which is on a plug top.
I think it probably wasn't fitted properly and has just been arcing inside but I'll be sending ideal an email
 
I thought it looked like a crimp, I assume from what you're saying it's a push-in connector.
 
they spin when on the end of the cables so there a load of carp.

shouldnt be able to twist them around the conductor.


it looks like the internal connection between the two push fit terminals has failed.

lever wago's or crimps are the way to go
 
I think that's the first one I've come across that's failed. They are pretty solid when you pull the two connected ends but if the connectors spin then they can loosen off
 
I think that's the first one I've come across that's failed. They are pretty solid when you pull the two connected ends but if the connectors spin then they can loosen off
that is the problem, we use pushfit connections all the time on danfoss inverters/pumps and they wont come loose if your wiggle or try to twist cable (same design as legrand switches)
 

Reply to Ideal 32a inline connectors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
729
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
492
Hi all. This is my first post on here so hopefully some of you will be able to suggest something other than my ideas. Worked as a spark for 19...
Replies
16
Views
3K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
30
Views
773
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock