It’s fairly common to find an open rings or a big spur ring where it was a ring and someone has added multiple Extra sockets off a single spurred cable So you have multiple sockets on a single 2,5 cable

from what I have seen on youtuber electricians most of then now just swap out the 32a mcb for a 20a mcb rather than try to put all the sockets back on a complete ring

but that imo is a bit lazy and you are reducing The Ccc of the circuit which Could have originally be designed to supply the whole house worth of sockets on a 32a ring circuit
 
That is a simple and cheap "fix" as you say, but not very elegant or professional.

Still, if the usual suspects from the kitchen (washing machine, dishwasher, etc) are on a different circuit I doubt most houses would draw 20A for the remaining sockets (unless they rely on a lot of plug-in electrical heaters, of course).
 
that's on reason for radials in the living/bedroom areas of a house. rare to see more than 5 -10 A anywhere except kitchen/utility rooms. RFC is the logical choice for the latter.
 
Maybe 10% of rings I test are open or very poor reading. No real difference in whether it’s L,N or CPC.

Never seen thermal damage due to open ring, and I’ve probably come across 100+ open rings over the years
 
I swapped a 32a device for a 20 on a recent job simply because rectifying the multiple spurs off spurs was going to be expensive and damaging. It's not always unprofessionalism, just the need to remedy at reasonable cost. I feel what is often forgotten on this forum in a rush to condemn a less than perfect solution is that not all clients can, or want to pay for the ideal when there is a cheaper way.
 
Which means that they usually get rectified, whereas the rings might not until the next EICR. Therefore if the probability of a connection being open is equal for rings and radials, EICRs would tend to reveal a disproportionately high number of faults on rings.

I previously raised the third question and no-one reponded with a confirmed case of thermal damage. I think there is a logical reason why none will be found. Cable CCC is based on a working temperature that will enable the cable to provide a good working lifespan under continuous load. It will withstand short excursions to significantly higher temps and is only likely to sustain visible damage if the insulation softens so much that it deforms at the connections or the conductors or cleats migrate through it. Any cable installed so that Iz is sufficient for a 32A RFC, will probably carry the full 32A by itself (or clear a fault on a B32) without this happening. It will remain in the zone where its working life and its ability to withstand mechanical damage is reduced, but won't actually disintegrate unless otherwise stressed e.g. by crushing. Since most general-purpose and domestic socket-outlet circuits are only ever fully loaded for brief periods, the reduction in durability will not tend to have any real impact and the cables will appear unharmed.
 
I’ve seen spec 4.00mm,mainly conduit cabling in schools.
If you go up another size you wont get the conductors in.
2.5 mm just the jobby.
Recently did a school block,spec,rings in classrooms,T&E,everywhere else radials 20amp 2.5mm
 
Also with rings I expect the majority of opens only impact on live conductor, so other other is still current-sharing as a ring and you don't have the full 32A thermal effect on one leg even if most of the loads are there.
[automerge]1598787515[/automerge]
It's not always unprofessionalism, just the need to remedy at reasonable cost.
My apoligies for that wording. On reflection it is not the right thing to say and as you point out sometimes making it safe at an affordable price is by far the best action.
 

Reply to Incomplete ring circuits? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This is a topic that comes up a lot and seems to attract near-religious levels of fever in how folks argue over the choice of circuit for UK...
Replies
54
Views
8K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Haven't been in the domestic side of things for a while.... I own a standard 3 bed house which is 30 yrs old 1x 50 amp cooker 1x 30amp RFC (for...
Replies
14
Views
2K
E
Hi guys. Ive generally no problem going through the deign process of cable selection for a circuit to be installed, (i try keep my hand in now and...
Replies
51
Views
12K
S
Here are useful LIGHTING CIRCUIT diagrams: WORD document of all common LIGHTING CIRCUITs...
Replies
12
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock