Discuss Induction/gas hob install in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part is 7kw max draw which is hard wired. The gas side comes with a 3 pin plug hard wired so it will need a socket. We wouldn't be able to have these on the same circuit because it is effectively a 10A socket on a 32A MCB. Can anyone see any issues having 2 supplies to 1 unit?
 
spur off the 6mm feed to the hob. FCU with a 5A fuse. then to a socket for the gas ignition, ssimples.
 
We wouldn't be able to have these on the same circuit because it is effectively a 10A socket on a 32A MCB
If that was a valid reason then these wouldn't be allowed:
1690271437227.png


I have in the past fitted one of these underneath as well in this situation and simply left them both turned on.

Another approach which is more elegant is to use a dual cooker connection unit. If you want no arguments from any future electrician then run 6mm to a single socket. The current draw from the gas hob ignition will be miniscule and the fuse in the plug will protect it.
I could construct an argument why < 6mm would meet the regs but sometimes it's simpler to make it obviously comply.
 
spur off the 6mm feed to the hob. FCU with a 5A fuse. then to a socket for the gas ignition, ssimples.

If that was a valid reason then these wouldn't be allowed:
View attachment 109546

I have in the past fitted one of these underneath as well in this situation and simply left them both turned on.

Another approach which is more elegant is to use a dual cooker connection unit. If you want no arguments from any future electrician then run 6mm to a single socket. The current draw from the gas hob ignition will be miniscule and the fuse in the plug will protect it.
I could construct an argument why < 6mm would meet the regs but sometimes it's simpler to make it obviously comply.

The OP is in New Zealand
 

Reply to Induction/gas hob install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
822
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
896
Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Replies
3
Views
2K
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock