Discuss Installation Reference Method in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi

What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?

Steve
 
method C unless it's an insulated wall that they're buried in.
 
Hi

What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?

Steve

Yes, Method 'C' from Table 4A2 of BS7671 page 320, reference number 58
 

Reply to Installation Reference Method in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys Is there a reason why installation ref method B (in conduit or trunking on a wall) not listed as an allowed installation method on the...
Replies
3
Views
821
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
577
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
I am interested in opinions on the following. Looking at GN3, page 126 the example of a Generic Schedule of test results lists the reference...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock