    Hi all,

    I am new to this forum and I need help installing what I believe is a two way dimmer switch. I have a single light bulb on the stairs which has a switch upstairs as well as two lights in the sitting room which are downstairs. Both the lights on the stairs and the two lights in the sitting room can be controlled via a double switch located downstairs. I removed the double switch and replaced it like for like with the new dimmer switch. Unfortunately, this didn't work as expected and the light upstairs doesn't fully switch off. The labels for the switch are as follows (pictures attached). I have also attached a picture of the new dimmer switch I bought.

    Two way switch located downstairs :

    Top section .... Common point (Red cable), L2 (Yellow Cable) L1 (Blue).
    Bottom section.... Common point (Red cable), L2 (Black), L1 is empty.

    Switch located upstairs for single stairs light.


    Common point (Red cable)
    L2 point (Yellow & Red cable)
    L1 point (Black and blue).

    IMG_20170903_122005.jpg

    IMG_20170903_122441.jpg

    View attachment IMG_20170903_110951.jpg

    View attachment IMG_20170903_114950.jpg
     
  2. rpm2
    Offline

    rpm2 Baby Gmes. Lol Electrician's Arms

    Location:
    uk
    Try changing the bulb if it is an energy saving type.
     
  3. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    I n your switch downstairs you will have a 3 core & earth cable,the earth should have a green/yellow sleaving over it and go to a earth terminal at the back of the metal back box, the red goes to common ,yellow to L1 and blue to L2.What wattage and lamp do you have in the light fittings ?

    More importantly make sure that you isolate (turn off ) both/all lighting circuits or if in doubt the consumer unit main switch.
     
  4. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    as above posts, note that if the new switch is metal, then the cpc (earth wire/s to the layman) should be connected to the earth terminal of the switch as well as or instead of to the back box.
     
  5. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    I am using a halogen like bulb which is similar to the one in my bedroom which works fine with a dimmer.
     
  6. rpm2
    Offline

    rpm2 Baby Gmes. Lol Electrician's Arms

    Location:
    uk
    Take it you haven`t tried then.
    A dimmer or the same maker & model?
     
  7. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Is the lamp you are using of greater power than the minimum load rating of the dimmer?
     
  8. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    Two way switch located downstairs :

    Top section .... Common point (Red cable), L2 (Yellow Cable) L1 (Blue).
    Bottom section.... Common point (Red cable), L2 (Black), L1 is empty
    .

    I suspect you have assumed that the 'top section' and 'bottom section' are the connections for each switch.
    In fact each switch has connections at the top AND bottom.
    ie common at the top, L1/L2 at the bottom.
    Although you state you have connected like for like if it doesn't work then clearly you haven't, it worked before.
     
    • Winner Winner x 1
  9. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    We are easily confused ... well I am at least :)
    I'm just going to say it - please ensure that power is off before you touch any of that. If you are going to touch the wiring, I recommend you turn off the board at the main isolator switch. There can be more than 1 live circuit in those backboxes !
     
  10. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Talking about confused - are you saying - the stairs light can be switched on /off from a single switch upstairs and one of the two switches downstairs? And the other two downstairs lights just switch on and off on the 2nd downstairs switch? And it's the downstairs two lights that you'd like to dim?
     
  11. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Just to be clear, Are you tring to put dimmers at both ends of this circuit? Or just at one end?
    >you have to buy special dimmers if you want to do this.

    Secondly. What are the terminal markings on the dimmer, what make & model is the dimmer.
     
  12. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    Thanks for the reply. I am trying to put a two way dimmer switch downstairs. This
    That is correct. I am trying to install the dimmer switch downstairs and this has two dim buttons on it. One button should be able to dim the lights in the sitting room and the other should be able to also dim the lights on the stairs. I am not touching the switch for the stair case light which is also upstairs.
     
  13. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Ok

    And

     
  14. darkwood
    Offline

    darkwood It's all about Gmes Staff Member Electrician's Arms

    Location:
    West Yorkshire
    Just to save the confusion, I have deleted the other duplicate thread and brought the reply posts into this thread, just in case you were wondering where a few replies had appeared from ;)
     
    • Like Like x 2
  15. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    So long as you have replaced the downstairs 2 gang switch by matching the cable positions into each terminal then this should be electrically correct.
    However, often a light bulb that is low energy is less than 60W, even a halogen energy saver, and this would be below the rating of the dimmer switch (60W to 400W) which may cause the dimmer to malfunction.
    Alternatively if the light bulb is an LED or compact fluorescent then there may be enough voltage on the cable to allow the light to flicker or pulse on even when the switch is off, although this may be expected to have been noticeable without the dimmer switch as well.
    Possibly the dimmer switch for the landing light is faulty and is not making the final switch off when switched and remaining at minimum brightness.
     
  16. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    OP - did the dimmer for the two lights in the sitting room work as expected?
     
  17. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    I'm not stating the blooming obvious when I say 'if the dimmer is a push to off, have you pushed to off?'
    If you have turned it right down to the lowest glow but don't push it to off then it'll keep glowing!
     
    • Like Like x 1
    • Optimistic Optimistic x 1
  18. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    Thanks for your help, this has now been resolved. Thanks
     
  19. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    • Agree Agree x 2
  20. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Maybe you were correct in #17.
     
    • Like Like x 1
  21. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    It's be sweet if it was - nothing better than getting to a customers house and having a resolve in 5 mins flat - even before the kettles boiled!
     
    • Like Like x 2
  22. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Would be nice to know as it may be something to be learnt by someone.
     
    • Agree Agree x 1
  23. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    How was it resolved. We are all interested!!
     
    • Agree Agree x 2
  24. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    Realised I was looking at the existing switch the wrong way. I was looking at the connections as top and bottom rather than left and right... The blue, yellow and red all to the right handle the light on the stairs, while the red and black towards the right handle the lights down stairs. I failed to see a middle vertical line between them due to cables. I assumed the top three were for one socket and the bottom three on the existing switch were for the other. All done, got the it working. Pics show it just as I want it.

    IMG_20170903_122005.jpg

    View attachment IMG_20170903_181414.jpg

    View attachment IMG_20170903_181611.jpg

    View attachment IMG_20170903_181620.jpg
     
    • Like Like x 1
  25. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Ahh common mistake. Glad it's sorted.
     
  26. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    Realised I was looking at the existing switch the wrong way. I was looking at the connections as top and bottom rather than left and right... The blue, yellow and red all to the left when looking from behind the switch all handle the light on the stairs, while the red and black towards the right handle the lights down stairs. I failed to see a middle vertical line between them due to cables. I assumed the top three were for one socket and the bottom three on the existing switch were for the other. All done, got the it working. Pics show it just as I want it.
     
  27. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Well done glad you got it sorted.
     
  28. pneme82
    Offline

    pneme82 EF Member

    Location:
    london
    One more thing to add on this case. Not sure if this is normal, but I fitted 100w=125w clear bulb Halogen by Status. When the lights are on and I turn the nobs to the left i.e, it does not completely go off. The only time it goes off is if I push it to turn it off completely. Also there is a buzzing sound which isn't really audible but can be noticed when you come close to the switch. Is this normal?
     
  29. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Yes.
     
    • Agree Agree x 1
Loading...
Similar Threads - Installing dimmer light Forum Date
Installing 2 PIRs on same circuit Electrical Forum Nov 12, 2017
Installing electrics in new build Electrical Courses & Electrical NVQ's Oct 8, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job