Hi,ard

I wondered if someone could give me a bit of advice please?

I'm fitting an electric hob to replace my old gas hob, which is fitted above an electric double oven.

The oven is hard-wired to a connection point behind it on the wall. This is fed from a standard cooker switch on the wall above with integral electrical socket. The cooker switch seems to have 6mm 2+E fed from a cooker circuit in my distribution box protected with a B32a mcb. The same type of wire then feeds the connection point at the back of the oven.

The current gas hob is hard-wired into a 3a fused connection point beside the oven connection point. This is powered from a multi-appliance panel itself powered from the standard downstairs sockets circuit protected with a B32a mcb.

Naturally, the existing hob point is not appropriate to run my new electric hob.

So in order to connect the new hob (6500w), should I:

- run a second connection from the cooker switch down to a new connection point mounted beside the existing oven connection, or

- change the existing oven connection box to a twin appliance connection box and connect the hob to that?

In either event, should I change the cooker B32 mcb in my distribution box to a 45a mcb?

Any thoughts would be much appreciated.

Paul
 
Hi,ard

I wondered if someone could give me a bit of advice please?

I'm fitting an electric hob to replace my old gas hob, which is fitted above an electric double oven.

The oven is hard-wired to a connection point behind it on the wall. This is fed from a standard cooker switch on the wall above with integral electrical socket. The cooker switch seems to have 6mm 2+E fed from a cooker circuit in my distribution box protected with a B32a mcb. The same type of wire then feeds the connection point at the back of the oven.

The current gas hob is hard-wired into a 3a fused connection point beside the oven connection point. This is powered from a multi-appliance panel itself powered from the standard downstairs sockets circuit protected with a B32a mcb.

Naturally, the existing hob point is not appropriate to run my new electric hob.

So in order to connect the new hob (6500w), should I:

- run a second connection from the cooker switch down to a new connection point mounted beside the existing oven connection, or

- change the existing oven connection box to a twin appliance connection box and connect the hob to that?

In either event, should I change the cooker B32 mcb in my distribution box to a 45a mcb?

Any thoughts would be much appreciated.

Paul
Paul you aren't an Electrician are you?
 
Hi Pete,

No, I'm not an electrician. Car mechanic initially. However, I'm reasonably competent and pretty safety-conscious.

Paul
then go by my post#2.it's not rocket science. basic competence will do.
 
Wilko,

yes, I have a variety of insulation, continuity and voltage testers. I might even still have some neon screwdrivers (which I won't be using).

Paul
shirley, you can use them for some terminations and to stir your tea/coffee.
 
telectrix,

Tks for your feedback. So even if I had both ovens going and all 4 rings are on the hob, do the diversity factors mean that my 32mcb can handle it?

Paul
 
telectrix,

Tks for your feedback. So even if I had both ovens going and all 4 rings are on the hob, do the diversity factors mean that my 32mcb can handle it?

Paul
yes. as the 32A MCB is rated to protect a 6.0mm cable, the worst that could happen is that the MCB tripped occasionally.
 

Reply to Installing Electric Hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
818
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
271

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock