Discuss Insulation resistance - strange readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
13
Im getting some strange reading on a new circuit(ring main) ive installed and i was wondering if anyone else had experienced the following.

insulation resistance at 500v on L-N is >500mQ (which is fine)
then insulation resistance between N-E starts at 400 then climbs to 500mQ
then insulation resistance L-E starts at 210 then slowly rises to 500mQ with the button held in.

There are no appliances connected and no sockets have been fitted at this point of testing.

Test meter is fluke 1625c (calibrated in november)

Quite bamboozled on this one
surely a damaged cable would get a bad reading and the reading wouldnt climb up to >500MQ eventually?
 
its an open new build site so you could say maybe some damp.
but its a ring test so ive connected all the points together and then i have the two ends at the boards so i dont know if damp can effect them.

nah i didnt null the leads

think the clips should be fine but i will re-check on that one.

My biggest fear is that somewhere, somehow, when ive been pulling them through joists thats ive got burning on the cables but i did try to take care, not overloading holes etc
 

Reply to Insulation resistance - strange readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
586
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730
Just done my exam, passed everything except Insulation Resistance... I can't think how I could've failed because it isn't the hardest thing on...
Replies
3
Views
2K
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock