Hi have AM2 next week and just need some help, 3 phase TP+N board, two way and intermediate lighting circuit with 3 switches obviously and one light, doing a global IR test, the lighting circuit say is on L1, so I’m testing all other circuits at once too do I have to switch my switches for every one of these tests
L1-L2,L1-L3,L2-L3,
L1-N,L2-N,L3-N,
L1-E,L2-E,L3-E, N-E
 
I'm not sure what the 'official' procedure for the AM2 is but from an electrical viewpoint, you test all permutations of 2 or 3-way switch positions to make sure each of the strappers and the SL get included in the test along with the PL. But they are only associated with whichever phase the lighting circuit is on, L1 in your example. So, if the switch wiring is not present in any accessories with any of the other phases, there would be no benefit changing the switch positions when testing L2 or L3 as the strappers and SL can't be faulted to those phases.
 
I'm not sure what the 'official' procedure for the AM2 is but from an electrical viewpoint, you test all permutations of 2 or 3-way switch positions to make sure each of the strappers and the SL get included in the test along with the PL. But they are only associated with whichever phase the lighting circuit is on, L1 in your example. So, if the switch wiring is not present in any accessories with any of the other phases, there would be no benefit changing the switch positions when testing L2 or L3 as the strappers and SL can't be faulted to those phases.
Ok thanks so if circuit is on L1 I’ll do,
L1-N,L1-E,L1-L2,L1-L3

So say if I do L1-N I’ll do,
Switch 1 ON test
Switch 2 OFF test
Switch 3 ON test then,
Switch 3 OFF test
Switch 2 ON test
Switch 1 OFF test
Then do the same for others
 
Ok thanks so if circuit is on L1 I’ll do,
L1-N,L1-E,L1-L2,L1-L3

So say if I do L1-N I’ll do,
Switch 1 ON test
Switch 2 OFF test
Switch 3 ON test then,
Switch 3 OFF test
Switch 2 ON test
Switch 1 OFF test
Then do the same for others
I haven't drawn it out but you only need to find positions where each of the line conductors will have been zapped.
 
Just sketch out the three switches and draw through the line conductors until all have been covered, those will be your combinations.
 
I have only done it in my head because I just link them together, but one test with them in one position and another with them all switched the other way, am I correct?
 
Ok thanks guys, the lighting circuit is feed to first switch then 3 core between switches then from last switch to ceiling rose so what I’ll do is,
Switch 1 off
Switch 2 on
Switch 3 off then test

Then Switch 1 on
Switch 2 off
Switch 3 on then test

So will I still have to do this for L1-E, L1-N, L1-L2,L1-L3
 
Doesn't really matter what position you have them in for the first test as long as you switch them all the other way for the second but yes you are correct.
 
Not sure about others views but I was always told when a switch is connected for two way operation it is never off or on, the lamp may be off but the switch still provides an output no matter its position.
 

Reply to Insulation resistance testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
848
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
619
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
448
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
479
I threw away an old knackered light switch and now need to replace it. It had 4 terminals (L1, L2, L3, L4) and is fed by two blue and two red...
Replies
8
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock