andyb

-
Esteemed
Arms
Reaction score
1,207
Had a call out yesterday to a house where the rcd on a board supplying storage heaters would trip intermittently. When I arrived the rcd would not reset at all. The rcd was also the main switch for the board.
Obviously an earth/neutral fault I thought, so with all the mcbs off and the the rcd off I did an IR test between n+e, result >999.
So a faulty rcd then, contemplating a 20 mile round trip to Electrifix I did what I thought was a pointless thing and disconnected the earth from the earth bar and reset the rcd. It stayed up. Touched the earth on the earth bar and the rcd immediately tripped.
Retested at the board and again got good results.

Any thoughts? I did solve it but it had me going for a while.
 
Anything to do with an appliance?

Without the earth connected, if there was a fault to earth then the RCD may not trip if its just relying on an earth path through the bonding which may be >1667. But you have tested to see if there was a neutral/earth fault!

I'll keep thinking.
 
Anything to do with an appliance?

Without the earth connected, if there was a fault to earth then the RCD may not trip if its just relying on an earth path through the bonding which may be >1667. But you have tested to see if there was a neutral/earth fault!

I'll keep thinking.

No, as I said there were no faults on the circuits.
 
My next test was also a silly test,

I tested between earth and the outgoing neutral on the rcd and got a fault.
Then tested again at the neutral bar and there was no fault.
They were connected by a solid copper conductor.
 
I think I'm going mad by now, I removed the solid link and the fault had disappeared from the rcd completely. Still no fault on the neutral bar.
Replaced it and the fault returned.
 
It was a Crabtree board with the earth and neutral bars extremely close together. Just 1 or 2mm apart.
The neutral bar had become loose and was intermittently touching the earth bar, When I tested the neutral bar to earth my probe was pushing it away from the earth bar so no fault.
When I took the probe away they were making contact again so I got a N/E fault just a few inches away on the switch.
Easily sorted once discovered, glad I never shot off to Electrifix.
 

Reply to Interesting Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock