Discuss Interlocking conveyors and motors in the Electricians' Talk area at ElectriciansForums.net

Reaction score
9
I'm going to be learning to interlock conveyors so that one cant start without the preceding one running. For safety purposes.

I'm working with a guy that does this all the time and we wont be doing this until next Saturday but he isn't the best at explaining stuff. He knows his stuff and is a fantastic spark but maybe I just don't absorb it all when hes explaining it.

The way I have it in my head at present is that if I have a contactor and overload (motor 1) with everything connected as should and then an additional conveyor needs installed. So new contactor and overload provided. Would I be right that I can loop my A2 from the first contactor for motor 1 to motor 2. Then can I loop from my A1 through a NO front mounted auxiliary onto the A1 of motor 2 contactor? Thus when motor 1 has been energised it lets A1 through to motor 2 so it can wait for a start signal?
 
Not quite; if you fed motor 2's contactor coil A1 directly from the contactor 1 auxiliary, it would start as soon as motor 1 starts. For a simple interlock, visualise each contactor with its own start and stop buttons arranged as usual, but add the NO auxiliary contact on contactor 1 in series with the motor 2 stop button. That way unless contactor 1 is energised there's no feed to either the start or hold contacts of contactor 2's circuit, just as if someone was holding in the stop button.
 
I'm going to be learning to interlock conveyors so that one cant start without the preceding one running. For safety purposes.

I'm working with a guy that does this all the time and we wont be doing this until next Saturday but he isn't the best at explaining stuff. He knows his stuff and is a fantastic spark but maybe I just don't absorb it all when hes explaining it.

The way I have it in my head at present is that if I have a contactor and overload (motor 1) with everything connected as should and then an additional conveyor needs installed. So new contactor and overload provided. Would I be right that I can loop my A2 from the first contactor for motor 1 to motor 2. Then can I loop from my A1 through a NO front mounted auxiliary onto the A1 of motor 2 contactor? Thus when motor 1 has been energised it lets A1 through to motor 2 so it can wait for a start signal?

I've worked on miles of conveying, carrying bottles, cans, airport baggage, pallets, frozen pies, quarried stone, etc etc and never is it as simple as that. Depending on whats being transported, there will be timers and sensors, and usually a PLC to control it.

Anyway, yours may be different.
 
from what i remember its the last conveyor that starts first and first one last so that the conveyors are running before any product is loaded on to them , and when stopping its the first conveyor that stops first
 

Reply to Interlocking conveyors and motors in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hello I'm Ronald Alliy, I have current came up with what I believe is a Infinite Electricity source. Attached is my proof. I'm a noob at blender...
Replies
12
Views
1K
Good evening all Ive got an old truck 1990 that has always had intermittent starting issues whilst ive owned it.. As far as i am aware the...
Replies
11
Views
906
Having to wire around a messed up output for a month or so. Some sort of program corruption is keeping the central lubrication system from...
Replies
3
Views
838
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock