Discuss IR readings Puzzeled in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
57
hi there

carried out IR test on radial lighting circuit today. L-N 700MOhms N-E 650Mohms L-E 320Mohms just wondered why the L-E would be nearly half the value ???? ( test carried out at 500v dc, TNCS system circuit disconnected at board)
 
320 meg Ohms is still massive, my Megger would just say >299Mega Ohms so hardly anything to worry about. A tiny thinner bit of insulation would account for it or perhaps a little moisture.
 
hi there

carried out IR test on radial lighting circuit today. L-N 700MOhms N-E 650Mohms L-E 320Mohms just wondered why the L-E would be nearly half the value ???? ( test carried out at 500v dc, TNCS system circuit disconnected at board)

Like Ian said 320Mohm is good. Was that with earth disconnected at cu? I've had some false readings when earth left connected with L and N disconnected...
 
jeez. it's like the captain of the titanic worried about the temperature of the 1st class swimming pool when it hit the iceberg.
 
if you breathe on the leads that can give you less than 300M.
 
Moisture in the air can give differing readings. Just about anything you can think of will give a variance.

To give you an idea I used to have to test a motor every week at 5KV DC. The records had a column for weather conditions. Like the Top Gear test track, it makes a hell of diference.
 
Moisture in the air can give differing readings. Just about anything you can think of will give a variance.

To give you an idea I used to have to test a motor every week at 5KV DC. The records had a column for weather conditions. Like the Top Gear test track, it makes a hell of diference.

as long as it's not that idiot clarkson doing the testing.
 
If you are looking for reasons why they vary so much

Then check how good the batteries are in the meter, if they are ok then check the test leads had quite a few which failed at the plug through the continuous flexing they get
 
maybe thayt's why my joints are failing... all this flexing.... not just bending to pull cables, but lifting beer as well.
 

Reply to IR readings Puzzeled in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
390
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
736
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock