Ive just in the process of doing a rewire and have been doing some circuit testing with my new megger 1710. On some circuits im getting IR readings of between 300 to 600 Mohm others and showing >999.
My questions are:
1. should I be getting >999 on all circuits as it's a new rewire or are reading of between 300 & 600 Mohm perfectly acceptable.
2. if they are not acceptable, what could be causing them
I know these readings are all way above acceptable levels, and would never have even shown up on my 1552, but i am just after a bit of clarification. The property has just been completely replastered, could the damp in the plaster be affecting the readings?

Many Thanks
Jon
 
Hi All

Ive just in the process of doing a rewire and have been doing some circuit testing with my new megger 1710. On some circuits im getting IR readings of between 300 to 600 Mohm others and showing >999.
My questions are:
1. should I be getting >999 on all circuits as it's a new rewire or are reading of between 300 & 600 Mohm perfectly acceptable.
2. if they are not acceptable, what could be causing them
I know these readings are all way above acceptable levels, and would never have even shown up on my 1552, but i am just after a bit of clarification. The property has just been completely replastered, could the damp in the plaster be affecting the readings?

Many Thanks
Jon
If you have fcu's with neon lights can affect readings and things like transformers for downlighters, energy saving bulbs. could be just enviromental factors!
 
agreed. just breathing on the leads could give that kind on a reading. bloody stupid these MFTs ranging to 999Meg. years ago >10Meg. was the norm. worry not.
 
The property has just been completely replastered, could the damp in the plaster be affecting the readings?

In a nutshell...........yes.
So if you think that's what it is then go and disconnect and test again.
If it's still flat tails get the hair dryer out:)
 
those are very good readings, no worries at all, if it is damp they usually climb slowly, The longer circuits will take a long time to 'charge' up to 1000 meg anyways, as has been said a tester need only read 200 anyway,
1 billion ohms is ridiculous!
 
On the auto test my Metrel goes up to 30M so I wouldn't even know if there were differences. Only when I use it on individual tests does the range go up to 1000M!
 
My questions are:
1. should I be getting >999 on all circuits as it's a new rewire or are reading of between 300 & 600 Mohm perfectly acceptable.

I know these readings are all way above acceptable levels,

[/QUOTE]
Obviously I've cut things out but Jon, have a word with yourself mate. Key things are knowledge, skill and confidence.
 
agreed. just breathing on the leads could give that kind on a reading. bloody stupid these MFTs ranging to 999Meg. years ago >10Meg. was the norm. worry not.

Don't you mean 100 Meg?? Can't think of any of the older analogue units i've used in the past, that were that low at the end of the range scale!!
 

Reply to IR Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
399
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
324
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
636
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
634

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock