Discuss Is a Fan isolator required in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Use a decent brand like Vortice and there is no need for the 3A fuse. Silliest thing I have seen is Bathroom Lights Fused down from 5A fuse/6A MCB to 3A fuse for the fan. Totally pointless exercise.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.
it would probably not have blown a 3A fuse either.
 
they specify a 3A fuse because they don't have a clue about OCPD discrimination. a 1A fuse would be more appropriate.

i'll give you a personal example. i had a vivarium with a 250wall heat/light reflector lamp. plug fuse was 5A. when the lamp blew, it took out the 16A MCB in the CU, leaving the 5A fuse in the plug intact.
 
Presumably the collapsing filament produced a near short circuit, otherwise nothing would have blown/tripped. Under those circumstances a type B MCB probably would trip faster than a plug fuse would rupture. The stuck fan motor would pass a sustained current of a few amps which is a completely different scenario.
On a related subject, there have been many threads on here concerning MCBs in series, and their lack of discrimination. While this may be true when short circuits are considered, a lower rated second MCB in the chain will discriminate against overload.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.

Then the manufacturer should have fitted appropriate protection within the fan, the ocpds we install are not there to protect appliances, they are there to protect the cables which feed the appliances.
 
Not sure I'd like to argue that in front of a Coroner's court.
Fortunately, in the case I referred to, no Coroners were involved, although the property in question received serious damage to its roof, and presumably, water damage throughout the rest of the house.
I normally only fit triple pole fan isolators alongside in line fans in lofts, and supply the whole lighting circuit to the bathroom through a switched FCU, fitted with a 3A fuse as per most manufacturers instructions.
Wall mounted fans, which I try to avoid because of their comparatively poor extraction rate and noise, just get the switched FCU.
 
Not sure I'd like to argue that in front of a Coroner's court.
Fortunately, in the case I referred to, no Coroners were involved, although the property in question received serious damage to its roof, and presumably, water damage throughout the rest of the house.
I normally only fit triple pole fan isolators alongside in line fans in lofts, and supply the whole lighting circuit to the bathroom through a switched FCU, fitted with a 3A fuse as per most manufacturers instructions.
Wall mounted fans, which I try to avoid because of their comparatively poor extraction rate and noise, just get the switched FCU.

Not sure I'd like to be a manufacturer in court explaining why the product I had designed and sold did not have adequate protection for its design.
 
Not sure I'd like to be a manufacturer in court explaining why the product I had designed and sold did not have adequate protection for its design.
Agree Andy, but it doesn't seem to stop them. Many extractor fans and dryers are still made without thermal overloads, which is strange given their proximity to dust and fluff that jams them from time to time.
 

Reply to Is a Fan isolator required in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
785
Hi to all, If extractor fan in bathroom is autonomous does it still require isolator switch or usual fused switch will do? It runs of 12v...
Replies
5
Views
3K
Hi I have bought a new bathroom fan to replace a faulty one. I don't have much cable available (emerging from wall) and it won't stretch to the...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock