Is it ok to have PV system into shared (household) RCD?

So I've had a system installed, but not yet complete/signed off. The issue is that the PV (and a car charger) are wired into a shared RCD (with water heater, boiler and downstairs sockets). When all breakers are on, the system trips. It works when either sockets or PV system are off.

From what i have seen (from my light research), it generally bad practice to be putting the PV (and presumably EV charger) into a shared RCD. Secondly, if it were to be in a shared RCD, then it should be a type B.

Issue is that there isn't space to put anything more into the fuse box, so would require another external box. It may be possible to free up a space if I can replace the door bell transformer with a single size unit.



Inverter: solaxpower.com/x1-boost/

Battery: alphaess.com/smile-b3-plus-3kw-residential-energy-storage-system

Charger: myenergi.com/product/zappi-ev-charger/
 
Can you show a picture of your consumer unit.
Here! The 2 on the left are the new additions. The car charger was freed up by putting the downstairs lighting in with the upstairs on the other RCD. Thanks
BAE823BF-3092-4623-A2D9-44CD3DE51957.jpeg
 
Last edited by a moderator:
That's the solar stuff. No idea why it's called that. What makes it incompatible? Would that explain why it's tripping?
It should be a Hager device not Steeple, FB2 would probably mean Fuse Board 2 but that isn't causing the tripping. Tripping could be an excess of leakage from the combined circuits or a fault.
 
It should be a Hager device not Steeple, FB2 would probably mean Fuse Board 2 but that isn't causing the tripping. Tripping could be an excess of leakage from the combined circuits or a fault.
That's what he's been saying - that existing socket circuit had too much leakage and the PV system in addition is too much.
But you are saying it's unsafe and doesn't meet the regulations to be on the same circuit? I want to have a clear plan of what I need to ask for.
I think there needs to be an additional fuse board with an RCD each for the PV and charger? Is that right?
 
That's what he's been saying - that existing socket circuit had too much leakage and the PV system in addition is too much.
But you are saying it's unsafe and doesn't meet the regulations to be on the same circuit? I want to have a clear plan of what I need to ask for.
I think there needs to be an additional fuse board with an RCD each for the PV and charger? Is that right?
No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.
 
No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.
Yikes, that sounds expensive, no? Is there not another (safe and legit) way? Or am I missing something?
 
Your installer should be providing you with a fully compliant installation.
If it is not suitable to connect to your existing distribution board, they should have come up with a plan that suits you, your budget and remains compliant.
if the 3 things listed above can't be done at quote time, the job should not have been started.
 
Your installer should be providing you with a fully compliant installation.
If it is not suitable to connect to your existing distribution board, they should have come up with a plan that suits you, your budget and remains compliant.
if the 3 things listed above can't be done at quote time, the job should not have been started.
Thank you. Yes I agree and assumed that this was what was happening.
Just hoping there might be another compliant option which would be less costly. Would an additional board with dedicated RCDs not be compliant (and a lot less work)?
 
The easiest and cheapest work round option from what I can see is to remove the right hand RCD and mcb's and replace those 3 with RCBO's then use the two slots from the RCD for the solar and charger so only costing you for 5 Hager rcbos. This would then solve the issue with the wrong MCB that has been fitted!
Personally I would do what @westward10 suggests earlier and replace the whole lot with a new SPD protected type A rcbo populated board with some spare ways in for future expansion!
Sy
 
On the subject of Hager RCBO's specifically for Solar PV, they are not bi-directional. Meaning they can not be reverse fed and shouldn't be used. I had this confirmed by Hager technical support.
For my solar install I am going to use a separate RCCB (RCD) and MCB specifically for the solar PV circuit.
 
On the subject of Hager RCBO's specifically for Solar PV, they are not bi-directional. Meaning they can not be reverse fed and shouldn't be used. I had this confirmed by Hager technical support.
For my solar install I am going to use a separate RCCB (RCD) and MCB specifically for the solar PV circuit.
Do you have any recommendations for RCCB and MCB combination and CUs that you would recommend in this situation?
 
Do you have any recommendations for RCCB and MCB combination and CUs that you would recommend in this situation?
As you can appreciate each setup is unique in what you need to specify for over current protection and whether RCD protection is required.

If you are unsure, you should seek the advice of a professional!

That said, if RCD protection is required you need to establish if there is simple separation between the AC and DC side of the inverter(s). If there is not, a Type B RCD will need to be specified to respond to DC currents >6ma.

The RCD will also need to be double pole, so that protection of the circuit is not reliant on the shutdown characteristics of the Inverter(s).

The manufacturer of the Inverter will be able to provide specifics on the inverter characteristics which will inform the protection required.

The solar setup I propose uses Enphase IQ7A microinverters. They do have separation between the AC and DC circuits.
So, 11 IQ7A inverters will need a 20A MCB and a 2P Type A RCCB. These will likely be Hager branded.

It is worth checking with the manufacturer of the devices to ensure they conform to the requirements of the instillation.
 
As you can appreciate each setup is unique in what you need to specify for over current protection and whether RCD protection is required.

If you are unsure, you should seek the advice of a professional!
Indeed and I am, but a lot of electricians are not familiar with inverters either.
That said, if RCD protection is required you need to establish if there is simple separation between the AC and DC side of the inverter(s). If there is not, a Type B RCD will need to be specified to respond to DC currents >6ma.
I have confirmed that there is some internal protection, the manufacturer states that IF an RCD is required then it should be Type A but with a higher trip current.
The RCD will also need to be double pole, so that protection of the circuit is not reliant on the shutdown characteristics of the Inverter(s).

The manufacturer of the Inverter will be able to provide specifics on the inverter characteristics which will inform the protection required.

The solar setup I propose uses Enphase IQ7A microinverters. They do have separation between the AC and DC circuits.
So, 11 IQ7A inverters will need a 20A MCB and a 2P Type A RCCB. These will likely be Hager branded.

It is worth checking with the manufacturer of the devices to ensure they conform to the requirements of the instillation.
I think I misunderstood your original comment that Hagar RCBO's were not suitable, I assumed you meant Hagar in general but I think you just meant their RCBOs.
 

Reply to Is it ok to have PV system into shared (household) RCD? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, I have a solar 5kw system installed with a hybrid inverter (no batteries yet). My electrician decided to add an extension board for the...
Replies
18
Views
5K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi all. First time poster here with a hell of a lot less hair than I had 3 weeks ago now! so please be nice, I'll try and explain best I can. I...
Replies
44
Views
15K
hi all just want to check this set up. have 17th edition board (already installed) have main switch then a VO on one circuit (hold fire read...
Replies
3
Views
9K
A
Does a PV system have to be RCD protected? I did a number of PV installations with a very experianced electrician who said that the PV system had...
Replies
28
Views
31K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock