Thank youThe Code of Practice for EV charging states that "Every charging point shall be individually protected by an RCD...."
Page 53.
In other words, not by an RCD that also protects other circuits.
Discuss Is it ok to have PV system into shared (household) RCD? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Thank youThe Code of Practice for EV charging states that "Every charging point shall be individually protected by an RCD...."
Page 53.
In other words, not by an RCD that also protects other circuits.
No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.That's what he's been saying - that existing socket circuit had too much leakage and the PV system in addition is too much.
But you are saying it's unsafe and doesn't meet the regulations to be on the same circuit? I want to have a clear plan of what I need to ask for.
I think there needs to be an additional fuse board with an RCD each for the PV and charger? Is that right?
Yikes, that sounds expensive, no? Is there not another (safe and legit) way? Or am I missing something?No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.
Thank you. Yes I agree and assumed that this was what was happening.Your installer should be providing you with a fully compliant installation.
If it is not suitable to connect to your existing distribution board, they should have come up with a plan that suits you, your budget and remains compliant.
if the 3 things listed above can't be done at quote time, the job should not have been started.
Do you have any recommendations for RCCB and MCB combination and CUs that you would recommend in this situation?On the subject of Hager RCBO's specifically for Solar PV, they are not bi-directional. Meaning they can not be reverse fed and shouldn't be used. I had this confirmed by Hager technical support.
For my solar install I am going to use a separate RCCB (RCD) and MCB specifically for the solar PV circuit.
As you can appreciate each setup is unique in what you need to specify for over current protection and whether RCD protection is required.Do you have any recommendations for RCCB and MCB combination and CUs that you would recommend in this situation?
Indeed and I am, but a lot of electricians are not familiar with inverters either.As you can appreciate each setup is unique in what you need to specify for over current protection and whether RCD protection is required.
If you are unsure, you should seek the advice of a professional!
I have confirmed that there is some internal protection, the manufacturer states that IF an RCD is required then it should be Type A but with a higher trip current.That said, if RCD protection is required you need to establish if there is simple separation between the AC and DC side of the inverter(s). If there is not, a Type B RCD will need to be specified to respond to DC currents >6ma.
I think I misunderstood your original comment that Hagar RCBO's were not suitable, I assumed you meant Hagar in general but I think you just meant their RCBOs.The RCD will also need to be double pole, so that protection of the circuit is not reliant on the shutdown characteristics of the Inverter(s).
The manufacturer of the Inverter will be able to provide specifics on the inverter characteristics which will inform the protection required.
The solar setup I propose uses Enphase IQ7A microinverters. They do have separation between the AC and DC circuits.
So, 11 IQ7A inverters will need a 20A MCB and a 2P Type A RCCB. These will likely be Hager branded.
It is worth checking with the manufacturer of the devices to ensure they conform to the requirements of the instillation.
Reply to Is it ok to have PV system into shared (household) RCD? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net