Discuss Is this RCD underrated? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Looking to add two circuits for a workshop & an outside socket, but in looking at my CU there are four MCBs; (one 32A ring, two showers 40 & 45 and 32 cooker) into an 80A 30mA RCD. I appreciate the likelihood of running both showers, oven, washing machine and tumble drier simultaneously is unlikley, but is this common practice?
We have experienced it tripping when all appliances are on & our two boys are growing=increasingly showering! - probably only going to get worse.
 
Looking to add two circuits for a workshop & an outside socket, but in looking at my CU there are four MCBs; (one 32A ring, two showers 40 & 45 and 32 cooker) into an 80A 30mA RCD. I appreciate the likelihood of running both showers, oven, washing machine and tumble drier simultaneously is unlikley, but is this common practice?
We have experienced it tripping when all appliances are on & our two boys are growing=increasingly showering! - probably only going to get worse.
Is this RCD the main switch?
 
Looking to add two circuits for a workshop & an outside socket, but in looking at my CU there are four MCBs; (one 32A ring, two showers 40 & 45 and 32 cooker) into an 80A 30mA RCD. I appreciate the likelihood of running both showers, oven, washing machine and tumble drier simultaneously is unlikley, but is this common practice?
We have experienced it tripping when all appliances are on & our two boys are growing=increasingly showering! - probably only going to get worse.
Hi Dave and Welcome to the Forum :)
I wouldn't install 2 showers on one RCD. If they ever go on together that will be close to full capacity and a toaster and kettle will see you OTT.
 
Well, yes, it didn't seem right, but someone disagrees with both of us and has done! Install was before we moved in.
Resolve with an independent 45A RCBO for each shower straight after the main switch, or anyone have a better idea?
 
As above your set up is not ideal .If its an RCD and not and RCBO then that would only trip if there where a fault as in to much earth leakage, it will not trip out if overloaded
 
Just move one over onto a RCBO and save the cost of a second RCBO!

Long term would be better with independent RCBO's as potential problems would not affect other circuits.
 
What power are you looking to add to work shop? As others have said you could just add rcbos for your addional circuits, depends on the make of you board though as some rcbos may cost the same a new consumer unit
 

Reply to Is this RCD underrated? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

quick question, 80a/30ma rcd protecting 5 32a circuits 2 ring mains 1 oven 1 shower 1 hob ive been told the shower and hob need upgraded to 40a...
Replies
26
Views
3K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...
Replies
12
Views
3K
Background: I have a ex council 1st floor flat that I bought, I moved in to care for my disabled mum and so rented the flat as I could not do...
Replies
34
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock