dansk

-
Reaction score
756
Im getting myself all confused and want some help.

Inverter is 20A max input current.

I have the following:

Isc 5.72 per string x 3 = 17.16 for the array at stc, inverter is is 20A max DC input, but when i apply 1.25 factor this gives 21.45, so is this inverter not the correct one? or will it be ok?
 
Well what im getting confused about - is the array Isc is 17.16 at stc, but to make sure the DC main cables are rated properly we apply 1.25, so does this mean the DC input from the array could be as high as 21.45A? in which case the inverter input is 20A so do i have this right?

Another way to look at it - is the Isc affected by tempreture like the voltage?
 
The 1.25 factor is oversizing to allow for carrying fault current (because fault current is not much higher than normal operating current, other forms of overprotection aren't suitable. I don't think this factor needs applying to inverters.... although I could be wrong.
 
Ok - So the Isc is the max current that will flow into the inverter. So if the inverter is rated at 20amp and the array Isc is 17.16 im ok then.
 
The 1.25 multiplication factor is applied to the array short circuit current, Isc, and gives you a theoretical maximum figure that you could expect to see here in the UK. (Isc is specified at standard test conditions by manufacturers and in reality, under certain conditions, can go higher).

You need to multiply your Isc value by 1.25 and ensure that this is within the max. current handling capacity of the inverter.

You do not multiply the inverter rating by 1.25.
 
"You do not multiply the inverter rating by 1.25" - understood. It was the 1.25 on the array Isc, so my 17.16 x 1.25 = 21.45A and my Inverter is 20A max - so in this case its not going to work.
 
bummer. its getting a bit late in the day now to be swapping inverters.

Thats something you need to watch on PV-SOL ive just learned.......its says its ok, but in reality its not!!
 
Not used PV-SOL but does it set the array default operating temperature range to -10 to +60 degrees? If so, that may be why it's showing the design is OK. You need to use the temperature range -15 to +80 degrees here in the UK (that's where the multiplication factors of 1.25 on current and 1.15 on voltage come from)
 
Mines set to -10 to +70 but thats only for the Voltage, when checking current it only checks at stc. it doesnt use any correction factor - but i will.

Whats the worst that could happen - i guess the inverter will shut down is theres an over current.
 
I suppose the inverter will either shut down or go pop. Assuming the array current ever gets that high in the first place. Don't know how likely that is to be honest.

Correction to my earlier post: it is the Voc value that is primarily affected by temperature, which is where the 1.15 factor comes in. The biggest effect on current is insolation. stc values are at 1000W/m2 but we have to account for levels up to 1250W/m2. Since the Isc output of a module is pretty much proportional to insolation, this is where the 1.25 factor comes in (1250/1000).

Man, I need to stop thinking about this stuff and watch some mindless crap on the tele.
 
Is it not impossible to get a short circuit current at the inverter? It's either short circuited, and therefore bypassing the inverter or connected to the inverter as a load?
 

Reply to Isc and Max Input Current on Inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
444
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hello!! I am using 2 ABB 100kw string Inverters (ABB PVS 100-TL) in a single room. Can anyone assist me in calculating the Heat dissipation from...
Replies
1
Views
6K
I have 2 arrays on 2 SMA inverters. One is 500v single string and the other is paralleled 2 x 300v strings. I have just lost one of my arrays via...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock