I have a question regarding isolation and switching arrangements.

I want to work out what would work best within the regulations regarding splitting a new 200a TPN PME supply to serve flats above and a shop below.

my initial thinking new 200a PME supply - Trunking above feeding a new ryefield giving me x2 100a 3 phase supplies. (2x100a 3 phase supplies)
I would then have a x2 100a un- fused isolators for the shop and flats

*will i need an isolator between the Ryefield and the service head
*does the above sound feasible?
 
Sounds like you are being the BNO. UK power networks have a good guide on this as I have been in a similar situation. Make sure you are in contact with the DNO and what their requirements are. Some DNOs may ask for a 3 phase isolator before the ryefield. If its a small install you may get away without one. I fitted switch fuses to my risers.
 

Reply to Isolation and switching in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
880
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
586
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
772
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock