Hi,

I have 6 spotlights in my bathroom, when I moved into the house 4 years ago I replaced all 6 with LEDs but they wouldn't work, turns out I could only get the lights to stay on if 2 Halogen bulbs remained (1 on each end of the bathroom). Recently one of the 2 Halogen bulbs has died and now none of the lights come on. When you turn them on the LEDs all flicker once then stay off. My Halogen bulbs were 20W and the LEDs are 3W-25W. Is there a maximum load for all six that i'm going over when using 6 LEDs or something? I'm a complete novice when it comes to electrical matters.

I would just try 20W equivalent LEDs but I can't find them in shops.

Any help would be appreciated.


Thanks,
 
i would replace all bulbs/fittings with 240V, either GU10 or integrated fittings and bin the transformers. I cover Stoke, so could easily give you a quote.
 
Most smps require a minimum load to function correctily,
if you try a load smaller than that, it may or may not work,
i suggest your load on your smps is too small
try changing your smps for one designed for the smaller load.
 
i recently bought a pack of 12V MR16 LED lamps that are happy running from the existing halogen transformers, bench testing showed no signs of flicker. not yet tried to see if they are dimmable though.
 

Reply to Issue with having all LED spotlights in bathroom, 2 must remain Halogen in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
488
I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
905
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
406

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock