Discuss IT earthing system cable calculation in the Electrical Engineering Chat area at ElectriciansForums.net

Lc1

-
Reaction score
22
Hello,
Does anyone know if Trimble can be used for cable calculations for equipment with an IT earthing system? If not could you please point me in the direction of an example calculation if possible.

Thank you
 
IT systems are usually very specific cases like ships or medical facilities. The normal CCC & VD aspects are the same but they obviously don't have the same conditions for earth-fault ADS as often that is the whole point - not to disconnect on a single fault!
 
Thanks for this. Could you point me in the direction of an example calc as I do not believe this can be done on Trimble and I have just asked for a trail of electrical OM.

Thanks again.
 
What are you trying to calculate, and for what sort of system?

IT systems are either small for single loads like shavers, etc, or if larger and multiple loads they normally have to be under skilled supervision and to have earth fault monitoring in place.
 
What are you trying to calculate, and for what sort of system?

IT systems are either small for single loads like shavers, etc, or if larger and multiple loads they normally have to be under skilled supervision and to have earth fault monitoring in place.
Still early on project but would be multiple loads “ large” loads and have earth fault monitoring.
Thanks again.
 
IT systems are usually very specific cases like ships or medical facilities. The normal CCC & VD aspects are the same but they obviously don't have the same conditions for earth-fault ADS as often that is the whole point - not to disconnect on a single fault!
I wouldn't mind seeing one in tht flesh as I find it hard to visualise it
 
Lister1987, IT Earthing Systems are common practice for offshore installations. See attached overview of one in the flesh
Interesting to see that, clearly most systems able to be isolated / alternate feed to keep going even if something has failed.

Also it looks like the "VFD" board (centre bottom) is really DC but 6-phase rectification (from the delta to delta+star transformers)?
 
I wouldn't mind seeing one in tht flesh as I find it hard to visualise it
Essentially there is no "hard" linking of a live conductor to earth to define neutral, so if any fault to earth then only a small current flows and you don't lose power at sea or during an operation, etc.

Simplest monitor in older / smaller systems was a pair of lamps (single phase) or 3 lamps (3-phase) from the live conductors to earth. If all was normal they would glow the same dim level, if one phase was faulted to earth it's indicator would go off and the other light glow at full brightness.

In that sort of a system it is not safe for shock as easily 30mA is available due to the lamps (and potentially just through capacitance in large system), but for the likes of medical use, etc, electronic monitors would be much higher impedance.
 
Interesting to see that, clearly most systems able to be isolated / alternate feed to keep going even if something has failed.

Also it looks like the "VFD" board (centre bottom) is really DC but 6-phase rectification (from the delta to delta+star transformers)?
Yes , redundancy through out. And yes the VFD board is all DC drilling equipment.

You can almost predict when the galley starts preparing meals, as the earth fault alarms ping through when they turn on the grills and hot plates lol!
 

Reply to IT earthing system cable calculation in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
620
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
417
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
357
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
686
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock