Discuss It has always worked fine.. what's the problem? in the UK Electrical Forum area at ElectriciansForums.net

MJPD29

-
Esteemed
Arms
Reaction score
3,067
Was asked to an EICR a building today, old church converted into workshop. This was 1 of 6 boards, this is how i found it. Was told it hasn't had a cover in 20 years and the last electrician passed it so what's the issue? Some people are unbelievable. To make matters worse it's at head height and not even hard to reach

20190401_153615.jpg
 

Reply to It has always worked fine.. what's the problem? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
556
Hello ! I am building for some time a cct to drive a 3digit multiplexed LCD. (from aliexpress) From the sellers on aliexpress I managed to find...
Replies
7
Views
1K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
949
Hi all. I have a G40PSH (Greenworks 40v Long Reach Cordless Hedge Trimmer) which I have taken apart before to sharpen the blades. Only this time...
Replies
3
Views
3K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock