Discuss It's the weekend so.... in the UK Electrical Forum area at ElectriciansForums.net

Not if they are in the bathroom (and its RCD protected)
 
No,because I am not working with cable tray,but
My thoughts are,most situations probably not,but
If the specs asked for them to be bonded then bonded they will be,but
I would say that they also need bonding if they enter/exit a building
 
Wouldn't cable tray be an exposed conductive part, assuming you can touch it??

Exposed-Conductive-Part – Conductive part of equipment which can be touched and which is not normally live, but which may become live under fault conditions.

If there was an Insulation resistance fault with a cable on cable tray, there would be potential of it going live, so personally I would bond it, but it could be out of reach??? meaning it can't be touched and doesn't require bonding??

Either way, I would still bond it to be safe.
 
Wouldn't cable tray be an exposed conductive part, assuming you can touch it??

Exposed-Conductive-Part – Conductive part of equipment which can be touched and which is not normally live, but which may become live under fault conditions.

If there was an Insulation resistance fault with a cable on cable tray, there would be potential of it going live, so personally I would bond it, but it could be out of reach??? meaning it can't be touched and doesn't require bonding??

Either way, I would still bond it to be safe.
If it was deemed to be an exposed conductive part then you would earth it not bond it.
 
Tray carrying insulated and sheathed cables would not be an exposed conductive part as the insulation and sheath are deemed to provide the same basic and fault protection as class II equipment 412.2.4.1
 
So SWA, Twin and Earth, MICC, SY, FP200 ext, Double insulated Flex, and Double insulated Meter tails would all be okay.

But if someone (Not me) was to run single cores or bare MICC, then it would need Earthing.
 
No,because I am not working with cable tray,but
My thoughts are,most situations probably not,but
If the specs asked for them to be bonded then bonded they will be,but
I would say that they also need bonding if they enter/exit a building
You think it is a good idea to bond a tray where it passes from a building, maybe into another.
 
Exactly what I have been reading haha. I didn't even know you can get bare MICC until I read that. Allways thought it was in an orange sheath.

Allways learning, that's what I signed up here for :)
I have installed bare, orange, red, black and white. Pay the manufacturer enough they will probably do you some pink.
 
Was there any particular reason for installing bare? or was it just down to cost / availability / Spec
Bare isn't common but you often see it in churches where the sheath tarnishes and becomes more aesthetically pleasing, in other words it blends to the surroundings.
 

Reply to It's the weekend so.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm probably displaying my ignorance here, but fortunately I'm not one of those people who can't stand to be laughed at! I've been thinking a bit...
Replies
27
Views
1K
So I’m an apprentice and only get to do downlighter jobs as foreigners at the weekend, but they’re typically added when the customer no longer...
Replies
23
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
So to try & keep confidentiality, a broad question without specifics; A manufactured bed, mechanically operated by electrically powered motors...
Replies
6
Views
851

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock