Hi everyone,

Sorry if this is the wrong forum for this question or it's too simple (mods please move if you need to) but I have had a new cu and sub-main installed (meter moved by dno) and the installer gave me an installation cert. with test results for the distribution circuit from switch-fuse in meter cabinet to new cu (moved 8 feet as the crow flies in bungalow) but no tests on re-connected final circuits. An EICR was done a few weeks beforehand, but there are new and old cables connected in JBs in the attic. Am I entitled to ask for tests on all final circuits? A local NAPIT spark and NICEIC say I am, what do you guys/gals think? I don't want to go off at half-cock or be ripped off.
 
If a consumer unit is moved and by what you are saying additional cables have been installed to extend the cables then you should have an installation certificate also you should have a notification certificate as this work is notifiable unless in scotland
 
^^^ just like Nick says + even if this was a c/u change without moving and extending circuits, it would need to be certificated and notified.
 
if it was a case of the existing CU being moved, then what you have is OK< but for a new CU, all the circuit parameters have been altered, so a full EIC including test figures for each circuit should be provided.
 
also you should have a notification certificate as this work is notifiable unless in scotland

Just to add to this comment, this can take several weeks to come through some times, so you may not have it if it's only just been done.
 
Thanks to everyone for replies so far. (thanks button pressed as well). Looking at names and numbers of posts and thanks given by others, I'm honoured. In reply to concerns/opinions, the guy who did the work is on checkatrade for 4 years with 10/10 rating, has C+G 2391 testing, 2382 requirements, is a part p supervisor, is an NICEIC DI (possibly more qualified than that), trust mark member.
@ Nickblake and uksparks: I've received the cert. from building control via NICEIC already (promptly too).
@ Telectrix: It is a new cu.

I just want to get my ducks in a row before I call him back to dot the Is and cross the Ts. It looks like this is black and white, not one the many grey areas there seem to be, but reputation matters and I don't want to be an a***h**e. I'm a white van driver myself, but it's my new house and I want the bits of paper I paid a lot of money for to be worth the ink they're printed with.
Thanks again for your time.
 

Reply to Lack of testing? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
826
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
726
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
888

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock