help needed please!

i have installed a 12v constant voltage, 16W LED driver with 3x 5w LED mr16 lamps but they keep going on-off! the driver does seem warm as if overloading. what am i doing wrong??
 
inrush current may be too high for the driver. try one around 30 or 40 watts.
 
Almost certainly overloading.

Power supplies and drivers are often rated by their consumption rather than their output capabilities. Also there's often derating figures supplied with them. I'd be looking at a driver at least 25% larger than the load it's supplying and if it's a cheap Chinese version you can make that figure nearer 50%.
 
Almost certainly overloading.

Power supplies and drivers are often rated by their consumption rather than their output capabilities. Also there's often derating figures supplied with them. I'd be looking at a driver at least 25% larger than the load it's supplying and if it's a cheap Chinese version you can make that figure nearer 50%.


thanks for the help and info. the driver is Halolite from screwfix. lamps are LAP also screwfix!
 
You might what to have a look at 'constant current v constant voltage'. The problem with buying lamps & drivers separately, as opposed a set made up by a manufacturer.
 
Are the mr16 the lap LAP 12v Led marked "direct replacement" If so I have had trouble with these they work ok on the old transformers perfect. So suspect they have some sort of regulating circuit built in for the ac from the trannies which uses up some power.
I returned these to screwfix.
lamp type I returned http://www.NoLinkingToThis/p/lap-mr...d=462033#product_additional_details_container
 

Reply to LED driver problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Does anyone know of a Driver for led tape that can adjust the brightness on the driver itself by turning a screw etc ? Just need...
Replies
12
Views
610
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
198
I have an old IKEA Norrsken 12v suspended ceiling tension wire system, which runs x7 20w MR16 bulbs, from a Min 4x20w/Max 10x20w transformer. Can...
Replies
5
Views
1K
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
753
Hello, I’ve have some ten year old Collingwood SL020 RGB led garden spike lights which I’d like to keep using but wondering if I can use them with...
Replies
0
Views
643

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock