Hi, just a quick one! I'm about to replace a halogen floodlight to a 10 Watt LED flood light, the switch inside the house has a pull out fuse under it, currently it's got a 13amp fuse in there, will that be OK for the new 10 watt LED light or should I put a 3 or 5 in there?

Thanks
 
Hi mate. Does it not mention what value of fuse to use in the flooflight manual. Check there first.
 
If not then post the make and model of the light.
 
You have to be careful Tazz, some of these 10W floodlight can have a Circuit Wattage of 11w.... :) pedantic.. me...
 
Weather 10w or 11w..there is 0.01 of amp in it......you are looking for a fuse rating not a technical specification....so 1-3 amp fuse would be good wouldn`t you agree
 
a 13A is fine if the cable is 1.5mm. any less, then downrate fuse to 5A.
 
Weather 10w or 11w..there is 0.01 of amp in it......

Looks like my little joke comment didn't quite come across like I intended.... :)
 
What do you expectr when we all gagging for beer.
 
Been a long few days....I of all members, should know to be more tolerant on the diy section

Yes you should Tazz now go and stand in the corner and face the wall
 

Reply to LED floodlight? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm from Sri Lanka. We have installed LED Floodlights from two different Italian Brands (I can mention the names if wanted) on two different...
Replies
1
Views
384
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
488
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
203
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
539
Hi all, I'm looking for a couple of PIR floodlights to replace old halogen ones, probably around the 50W mark would provide sufficient lighting...
Replies
1
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock