Discuss LED Panel Strange problem.. in the The Welcome Forum area at ElectriciansForums.net

Alex G

-
Reaction score
0
So a long story short, someone I work with said they had a small 'Tingle' off a Lumineux LED panel. We took a couple down that we recently installed, and plugged them into a safe tester to check if there was any voltage flowing through them. Oddly enough, we read 90-95V AC to earth, straight off the metal back of the panel. This is strange, as the Driver's output is only 38v DC. This was the same for all the fittings we tested. I spoke to Lumineux, but the guy thought I was crazy! Even if they were all faulty (they are all working fine) where is the 90VAC coming from?

Any Ideas?
 
Check the case and PSU are properly earthed. Switch mode PSUs usually have a capacitor between live and earth which provides part of an EMF filter I believe. This causes some leakage to earth. If the PSU doesn't have a good connection to earth this will appear as a voltage on any exposed metal parts.
 
Thanks for the reply... The LED Driver is double insulated and does not have an earth... The driver is not giving out enough voltage to cause the back panel to have 90V even if the fitting wasn't earthed properly. These are all plug and play so there isn't an option to earth the fitting, unless I did it to the grid it's placed on. but still... where is the 90V coming from :tearsofjoy:
 
Try measuring between the output terminals of the driver and earth. I think class 2 PSUs have the input and output coupled by a capacitor, again as a suppressor of EMI.
 

Reply to LED Panel Strange problem.. in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hey folks, i work for a relatively small company, but we are doing some big jobs. And right our headache is taking over outdoor lighting...
Replies
4
Views
1K
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
740
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
889
We have recently completed the installation of around 85 600x600 LED 25w Panels in a school, the panels are sited within ceiling grid which is...
Replies
2
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock