Discuss LED spotlight glowing dimly with power off in the Australia area at ElectriciansForums.net

Z

zerobug

I wondered if I could ask for some advice - I have a ceiling lamp fitting comprising 4 gu10 type 35w halogen spotlights. Some time ago I swopped the bulbs for LED versions which worked fine, but I decided to put the originals back for the darker mornings. When I took the led bulbs out, I noticed that when left with only one LED bulb in situ ( the other 3 holders empty) the one remaining bulb glowed, very very dimly, although switched off. On installing one of the original halogen bulbs into any of the other holders, ( still switched off) it went out. Could anyone suggest a cause as to why this might be happening? Cheers.
 
This phenomenon is caused by the final circuit cable capacitance. It is more common in conventionally wired two way and intermediate switching circuits due to the wide spread use of 3+E cable and the extra parallel capacitance that creates.
The GU10 mains LED lamp is essentially a number of LEDs driven by a constant current driver powered by a mains rectifier and smoothing capacitor.
Even though the live feed to the LED lamp is switched OFF the cable capacitance allows leakage current to flow to the lamp slowly charging the smoothing capacitor in the lamp until the potential is sufficient for the constant current driver to "fire" the LEDs. This discharges the smoothing capacitor, the constant current driver stops, the LEDs extinguish and the process of charging starts again ... if conditions are suitable this continues indefinitely.
In your case the charge/discharge cycle is short causing the LEDs to appear to be 'ON' continuously, however the energy is limited so the LEDs are only barely lit. Once more more lamps are added the loading on the cable capacitance is such that the individual smoothing capacitors do not reach "firing" potential.
A tungsten halogen filament lamp doesn't suffer this problem because the filament is permanently loading the cable capacitance and any acquired charge is unable to overcome the thermal inertia.
 
excellent , concise explanation, markie. or you could say it's the fairies.
 
or coulds it be those pesky faster than the speed of light neutrinos? ( used to get 'em in bags from the sweetshop )
 
this phenomenon is caused by the final circuit cable capacitance. It is more common in conventionally wired two way and intermediate switching circuits due to the wide spread use of 3+e cable and the extra parallel capacitance that creates.
The gu10 mains led lamp is essentially a number of leds driven by a constant current driver powered by a mains rectifier and smoothing capacitor.
Even though the live feed to the led lamp is switched off the cable capacitance allows leakage current to flow to the lamp slowly charging the smoothing capacitor in the lamp until the potential is sufficient for the constant current driver to "fire" the leds. This discharges the smoothing capacitor, the constant current driver stops, the leds extinguish and the process of charging starts again ... If conditions are suitable this continues indefinitely.
In your case the charge/discharge cycle is short causing the leds to appear to be 'on' continuously, however the energy is limited so the leds are only barely lit. Once more more lamps are added the loading on the cable capacitance is such that the individual smoothing capacitors do not reach "firing" potential.
A tungsten halogen filament lamp doesn't suffer this problem because the filament is permanently loading the cable capacitance and any acquired charge is unable to overcome the thermal inertia.


wow ! ! !
 
Ahhh thats why the upstairs compact fires off at night time , next question , how to stop it , apart from the filament lamp

Jamie

Hi Jamie, I didn't post a solution to the problem as it was irrelevant in Zerobugs situation. However, I do have a solution for you:

A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across the lamp holder terminals. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If this solution is implemented a notice should be placed at the DB stating which final circuits are effected and which lamp holders have been modified, why and how.
 
Last edited by a moderator:

Hi Jamie, I didn't post a solution to the problem as it was irrelevant in Zerobugs situation. However, I do have a solution for you:

A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across the lamp holder terminals. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If this solution is implemented a notice should be placed at the DB stating which final circuits are effected and which lamp holders have been modified, why and how.


Excuse my ignorance but would this be across just one within the circuit or each point. And in what way do you mean across terminals ? sorry i just intrigued and like to get clear in my head.
 
Last edited:
anywhere across L and N on the circuit. the resistors just act as a drain of the capacitance.
 
Excuse my ignorance but would this be across just one within the circuit or each point. And in what way do you mean across terminals ? sorry i just intrigued and like to get clear in my head.

Hi, Robinson, I've expanded the solution explanation to give you more information:
A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across L and N on the final circuit, it is good electronics practice to do this as close to the effected lamp as possible, if this is done across the switched L and N at the lamp holder terminals it allows simple switching out of circuit (or disconnection) for testing. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If the final circuit has a large number of switched lamps it may be pragmatic to connect the series resistors between permanent L and N at a convenient point e.g. at the DB to reduce the number of resistors required, however the number of points that will require treatment will depend on how the cable capacitance is distributed on the final circuit. Additional points particularly where 3+E is used for 2 way and intermediate switching may well require additional pairs of resistors.



 
Last edited by a moderator:
Hi, MarkieSparkie, seems pretty simple. I have this issue with a light fitting that I have just fitted with LED bulbs. I have have understood correctly you are suggesting 2 resistors at 160K (0.6W and min 250V) wired in series and then connected in parallel with the light fitting. Is that right? Only seems to affect this fitting so this seems to be the simplest solution.
 
MarkiSparkie,
Tried your resistor drain across fitting, made no effect, how does one calculate what value to use. This fitting now has 3 leds and all stay dimly lit after switch off. It is a two way circuit and all other criteria is as described. Help appreciated.
P
 
try the maplin snubber. link posted in post #12
 

Reply to LED spotlight glowing dimly with power off in the Australia area at ElectriciansForums.net

Similar Threads

I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
917
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Good afternoon! I've recently wired a lighting system, where one light switch (a motion sensor) turns on two lights, but another motion sensor...
Replies
3
Views
1K
The G4 110V 3W dimmable bulbs I purchased work with a dimmer. I can brighten them and dim them, but when I turn the dimmer off, the LED bulbs...
Replies
2
Views
928
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock